Verify these connections are actually L1 and L2.removed the plug and wire nutted strait to the tinned wires. L1 brown L2 blue yello/green ground.
Verify these connections are actually L1 and L2.removed the plug and wire nutted strait to the tinned wires. L1 brown L2 blue yello/green ground.
I was referring to this.If generator wasn't capable, it would choke on the load.
the generator will handle 70 amps but wants to stall @ 80 amps.
Might helpIf you call champion please update this thread as I'd like to know if I canodify the automatic voltage regulator to adjust. In the manual there is a set screw to adjust voltage but I days to adjust to 115v. I adjusted my governor already to give the 63hz required with no load.
Had I had the knowledge I had now before I purchased I would have bought the 14kw just to charge faster. Less wear and tear vs running the 8.5kw for a long period of time.
Nope! I did in fact F up its #12. What a bone head move! Maybe this was for the good? Learning lesson not gone bad yet. luckily I never ran the Magnum real hard. Also this generator portion of the wiring has not been installed as permanent or run for very long maybe 10 hours.I hope that it's #10.
That's what I found as well.From what I have found #4 and larger can be color tabbed.
Current/Power calculations are not rocket science. It's really simple ohms law: P(watts)=E(volts)*I(amps) and dirt simple algebra. We are holding the output constant, I'll use 60A @ 54v:I do expect more out of the DC side then 55 to 60 amps being powered by a 8500w generator. The way he explained it to me was the lower the ac volts in the more current it will draw. I’m by no means an electrical engineer or even an electrician. But the way he explained it made sense.
That was my first thought. But they wouldn't be able to charge above 50a from 120v.Reading the thread, it was a little unclear to me - was the OP trying to do 120v -> Chargerverter (instead of 240v)? If so, it would account for hi amps and not getting anywhere near 100a charging to the battery.
Those numbers look good. I'm guessing that the battery was around 53v.Update.
So today I replaced the #12 wire with #8. I even stopped by the electric shop and purchased green so I didn’t have to mess with color tabbing any. I connected the #8 wire nutted strait to the CV where I removed the plug. L1/brown L2/blue ground to yellow/green.
The generator still does the same thing. Con not charge above 70a DC on the Chargeverter.
Voltage and amperage as tested at the CV wire nut connection
Set point 60a DC output
227.4vac input
L1 15.78a
L2 15.71a
Set point 65a DC output
227.1vac input
L1 17.19a
L2 17.10a
Set point 70a DC output
226.9 to 227.2 input
L1 18.48a
L2 18.42a
I just installed one today with a 6500/5000 watt champion generator. The best the generator will do is about 3000 watts before it lugs out and generator cuts out the load. So out of my 5000 running watts I only get about 60% before the generator lugs out. Maybe Champion is a bit too optimistic...?Update.
So today I replaced the #12 wire with #8. I even stopped by the electric shop and purchased green so I didn’t have to mess with color tabbing any. I connected the #8 wire nutted strait to the CV where I removed the plug. L1/brown L2/blue ground to yellow/green.
The generator still does the same thing. Con not charge above 70a DC on the Chargeverter.
Voltage and amperage as tested at the CV wire nut connection
Set point 60a DC output
227.4vac input
L1 15.78a
L2 15.71a
Set point 65a DC output
227.1vac input
L1 17.19a
L2 17.10a
Set point 70a DC output
226.9 to 227.2 input
L1 18.48a
L2 18.42a
Yes about 53.7.Those numbers look good. I'm guessing that the battery was around 53v.
My 8.5kw is rated @ 35.4 amps. It was putting out 37 amps but don’t like it. I only did this for testing for about 30 seconds.I just installed one today with a 6500/5000 watt champion generator. The best the generator will do is about 3000 watts before it lugs out and generator cuts out the load. So out of my 5000 running watts I only get about 60% before the generator lugs out. Maybe Champion is a bit too optimistic...?
Do you mean 120v? or 240v? I think the twist lock outlets are usually for 30a @ 240v or 30a @ 120v.My 8.5kw is rated @ 35.4 amps. It was putting out 37 amps but don’t like it. I only did this for testing for about 30 seconds.
my generator is rated @ 230v but outputs 226-228v.Do you mean 120v? or 240v? I think the twist lock outlets are usually for 30a @ 240v or 30a @ 120v.
Mine was putting out about 14 amps at 240 volts. so 14a x 240v=3360 watts
It was putting out 18.5a.My 8.5kw is rated @ 35.4 amps. It was putting out 37 amps but don’t like it. I only did this for testing for about 30 seconds.
Update.
So today I replaced the #12 wire with #8. I even stopped by the electric shop and purchased green so I didn’t have to mess with color tabbing any. I connected the #8 wire nutted strait to the CV where I removed the plug. L1/brown L2/blue ground to yellow/green.
The generator still does the same thing. Con not charge above 70a DC on the Chargeverter.
Voltage and amperage as tested at the CV wire nut connection
Set point 60a DC output
227.4vac input
L1 15.78a
L2 15.71a
Set point 65a DC output
227.1vac input
L1 17.19a
L2 17.10a
Set point 70a DC output
226.9 to 227.2 input
L1 18.48a
L2 18.42a
You never reported actual readings of 37 amps. All the measurements previously were 15-18.4 amps.My 8.5kw is rated @ 35.4 amps. It was putting out 37 amps but don’t like it. I only did this for testing for about 30 seconds.
Ah got it.It was putting out 18.5a.
You are doubling your numbers.