As this is a 24V system set the following params.
Bulk/Absorb : 27.6V (3.450Vpc)
Float : 27.5V (3.437Vpc)
Your EndAmps/TailCurrent is 11.5A. when charge is only taking 11.5A switch to float mode
* EndAmps is when the cells are actually "full" at which time switching to FLOAT aka CV (Constant Voltage Variable Current) to top off and level the packs.
While this sounds good it has a few practical issues outside of an ideal setup.
27.6V is enough to top of charge at 3.450V yes, but it's not enough to leverage the balancer and come anywhere near solving top of charge imbalances. If all cells are at 3.450V you can call them charged, but I don't believe 27.6V and 11.5A will achieve that.
11.5A taper will never allow an 8S pack to balance without high voltage disconnecting a cell.
If you have perfectly matched cells and your daily cycle is shallow and always top down, then it might work out.
If you have poorly matched cells and your daily cycle is entirely weather dependant, often spending days and days in the lower 30% then it most likely will not work out. Even at that it comes down to your balancer and how you set it up.
Given an extreme case, I have a "weak cell". One of the 8 (no. 6) appears to have about 5% less capacity to it's peers (and maybe getting worse). Without longer absorb times and far, far, far lighter taper currents I will never get a top of charge in balance and I will be limited to 8 times the capacity of that weak cell -minus other balance loss. With longer absorb times and more dynamic top of charge current rating (with cell awareness) allows me to top balance the pack in normal operation and then continually balance it all the way down as well, such that when it spends a bunch of days between 10% and 30% it balances itself there and I gain more access to the low end capacity i would otherwise miss.
As soon as a single cell goes "vertical" on the chart you have two options. You terminate charge, shrug and call it good, leaving a mess behind.... or you limit the charge current to that which the balancer can fully control. If you have a 5A balancer, for example and a cell nears HVC you would need to limit the current to 2.5-5A. With a 5A Heltec I found that 1 Amp was needed to stop the runaway cell. The "across the pack current" is equal to the "across each cell" current. so at 5A, you WILL be pushing 5A into a full charged cell. It WILL 100% overvolt. Unless your balancer is capable of discharging that cell consistently at 5A you will need to go to a lower current.
Balance is more about the cell delta. it's also about how many cells are high/low. If it's a single cell that can lead to the worst case. A single cell being 0.5V higher than the others terminating charge. This is a different situation to having 4 out of the 8 high and 4 out of the 8 low. The later is easier to deal as you have 4 high cells sharing the current.