What is the optimal array configuration for 14 panels that are ground mounted?
14-455 Watt panels (49.35 Voc, 11.44 Isc)
one EG4 6500 EX controller/Inverter
offgrid only.
Charge controller:
Rated PV - 8000W
Max PV Array Open Circuit Voltage Input - 500Vdc
PV Array MPPT Voltage Range - 90Vdc~450Vdc
Solar array:
2 rows of 7 serially connected panels - can I connect 7 in serial?
49.35 VOC x 7 = 345.45 volts
11.44 ISC (amps) x 2 = 22.88 amps
Total watts = 345.45 x 22.88 = 7904W (below 8000W controller rating)