6 or 0 should work from what i was told in the pastAnyone running SOK or Jakiper batteries on EG4 18? Settings are lithium 0-19 with no explanation for what is what. I know it's pylon but don't which is that
Thanks
Ok thanks. Haven't tried yet.6 or 0 should work from what i was told in the past
with close loop you dont need to set that the BMS will tell the inverter those settingsOk thanks. Haven't tried yet.
I'm having a voltage difference from inverter to batteries. Up to .07 volts lower then batteries. Makes it hard to set absorption and float.
Im running lead right now. Once I get it figured out I won't. But right now I'm getting it setup on lead so I know it works. If it's anything like the 6548's they shut off if not right protocolwith close loop you dont need to set that the BMS will tell the inverter those settings
Start conservative. You can compensate for the variation by lowering voltage by 0.1v.Ok thanks. Haven't tried yet.
I'm having a voltage difference from inverter to batteries. Up to .07 volts lower then batteries. Makes it hard to set absorption and float.
Batteries have been in service for over a year. I'm just trying to get them to where they were with 6548's.Start conservative. You can compensate for the variation by lowering voltage by 0.1v.
Spitballing here. Without reading your battery manual.
I'd start with 56v and 54.5 float. If the batteries are brand new you may find it helpful to start at 54 and 54. (To facilitate quicker cell balancing)
I'd keep the charge rate under .2C until you have them balanced.
Yep, common. Very few people realize it. Not typically an issue when using closed loop.Problem is inverter is reading .5 volts less then Batteries and lugs where 2 runs of 4/0 go in.
Voltage matched on the 2 6548's. Wouldn't think a better inverter wouldn't be able to read the right voltage at lugs.Yep, common. Very few people realize it. Not typically an issue when using closed loop.
You would think.Voltage matched on the 2 6548's. Wouldn't think a better inverter wouldn't be able to read the right voltage at lugs.
ThanksYou would think.
Per a conversation that I had with LUX it's normal and can be seen on all of the "rebranded" LUX 12K. (aka working as designed)
Lux guy did say he would put in a change request for a calibration setting.
So today I ran my 4t AC. It worked a few times and now it shuts the inverter off. Have soft start and never had a issue before.You would think.
Per a conversation that I had with LUX it's normal and can be seen on all of the "rebranded" LUX 12K. (aka working as designed)
Lux guy did say he would put in a change request for a calibration setting.
I can look at your station if you DM me and make sure it’s set up properlySo today I ran my 4t AC. It worked a few times and now it shuts the inverter off. Have soft start and never had a issue before.
Waiting for them to escalate my problem to higher up