I have 20 250 watt used panels from San Tan
I am considering the EG4 6.5 KW 48 Volt ( 1 to start another in 6 months )

I am concerned about the Voltage Loss. Im very new to solar. I have read some forum posts on a few forums. There was some debate between running Solar Cable and AWG. So far it sounds like it is best to use Solar Cable from the panels 230 ft to the inverter. Input requested on these statements. Also input on the number of panels to run in series is requested.

Are all Solar cables the same thickness or do I need to buy a specific size for this run?

Is the fan noise on the newer EG4 6.5 Kw inverters still excessive?

I have a solar combiner box. I can use this if needed.combiner box.jpg
 
Last edited:
You're going to need the VoC numbers off the back of the panels to see how many you can get in series. You might be able to do 20s in one big array, then you can look up voltage drop calculators and start upping your wire size to get your voltage drop down.

You'll likely need to get some hefty direct bury and a junction block to get the PV wires connected to thick cable.
 
230 feet isn’t that far.
The size of wire needed primarily depends on current. Your inverter will accept voltages up to 500.
You should be able to run 300 volt or so strings without exceeding the 500 volt open circuit limitation. 2500 watts at 300 volts is only 8.3 amps.
South wire has a great loss calculator where you can see what the voltage drop will be. For 8.3 amps at 230 feet #12 would only be a 2.18% drop. Not big wire at all
 
As to which type of cable to run, how will it be installed?
In conduit use Thhn/thwn,not “solar” wire.
I was going to go overhead in the air on my fence and then into the attic space which has paper insulation. I was wondering if I would need to put the solar wire in conduit since my insulation is paper. Im not sure if that is at risk of heating or sparking in odd circumstances.
 
Looks like the flicker issue has been resolved.

 
You will need a disconnect where the conductors enter the building. And they will need to be in a metal conduit inside the building. The conduit will also need to be bonded.
 
You will need a disconnect where the conductors enter the building. And they will need to be in a metal conduit inside the building. The conduit will also need to be bonded.
I’m don’t think the disconnect has to be at the point of entry. Mine isn’t, and was inspected and approved.
 
I have 420 feet one way from array to house. Panels are 49.65VOC, I run 8 in series to one MPPT in the 6500EX with another 8S string to the other 6500EX.

The key is to keep VOC near the max VOC rating of the MPPT and amps down. I have 10AWG THWN inside buried conduit. I'm pulling max watts of 4Kw per MPPT in full sun.

For the combiner box, it isn't needed with a high VOC rated MPPT. You could still use the combiner for fusing strings, have a disconnect (breaker) and surge protection, just don't combine strings for higher amperage.

A 250W panel has a VOC of around 37V. 10 panels in series per string with one string per MPPT would work well. That would be 370VOC and low enough not to be concerned about cold weather.

If you are running wire overhead and exposed, you will need to run properly rated wire for sunlight resistance which does drive up the cost. Two concerns, one the high voltage is nothing to mess with on DC. Overhead wires always carry risk. Two, how are you planning on supporting the run of 200 feet?
 
Would microinverters help since they convert to A/C at the panel? I can't really find anything that says you can run longer distances over smaller wire though, so maybe not. https://www.ecowatch.com/solar/microinverters-guide
Microinverters would hurt, as far as minimizing wire size is concerned. They would limit the voltage to 240.
AC, when measured rms, takes same amount of copper as dc.
 
Would microinverters help since they convert to A/C at the panel? I can't really find anything that says you can run longer distances over smaller wire though, so maybe not. https://www.ecowatch.com/solar/microinverters-guide
Ah, nevermind, the dual conversion to AC then back to DC is inefficient. Carry on, nothing to see here!
Micros would be fine with some shading problems, the loss due to conversion might be easily made up.

Long distances can be run on small wire DC circuits by running higher voltages.
 

1680795930524.png

worst case 4000W array (max current, min voltage) per MPPT with a single pair of 10awg wires:

18A Imp
222Vmp

Not atypical for a 5S2P array of 24V panels around 325-350W.

3.73% voltage drop:


Arguably acceptable as that's only a 3.73% loss in power.

Single string of the same panels with 8 in series vs the 10 in 5S2P:

9A Imp
336Vmp

1.25% loss:


Point is this shit isn't rocket science. It can be calculated and there are many tools readily available to help the DIYer.
 
PV wires inside a building must be in metal conduit.
That's news to me. Not challenging it, but have a NEC citation? No PVC due to heat dissipation differences?

I am concerned about the Voltage Loss. Im very new to solar. I have read some forum posts on a few forums. There was some debate between running Solar Cable and AWG. So far it sounds like it is best to use Solar Cable from the panels 230 ft to the inverter. Input requested on these statements. Also input on the number of panels to run in series is requested.

Are all Solar cables the same thickness or do I need to buy a specific size for this run?

Is the fan noise on the newer EG4 6.5 Kw inverters still excessive?

Sabo,

The best way to do this is to push high voltage and less amperage. I didn't look up the specs on your panel, but you want high voltage (within the limits of the inverter). It's worth mentioning that high voltage DC is "more risky" to work with.

You need to run a "voltage drop calculator" once you know your string voltage / amperage. It'll help you select wire type. In general, you want to see less than 3% loss.

I have the EG-4 6500EX's. I do not find them excessive (but they are in my shop). They are louder than my Frontius inverter, but no where near as loud as a Dell Server, etc.
 
That's news to me. Not challenging it, but have a NEC citation? No PVC due to heat dissipation differences?
 
I’m don’t think the disconnect has to be at the point of entry. Mine isn’t, and was inspected and approved.
It doesn't necessarily have to be outside, but it has to as close to the point of entry as possible. You shouldn't, for example, run it through your house for 50 feet. It should either be on the outside, or immediately inside. Also, passing an inspection doesn't mean the install is code-compliant.
 