Oh right, the forum attachment setting will reduce the size of the image so they are not huge. I will increase it a tad.
And it looks good from a glance. What batteries are you using? Which inverter/mppt system are you paralleling?
How many amps is going into those mppts? Do you have shading issues? What is max input pv voltage?
For that size array you should probably put them in series. Bump up the voltage to 100-150 minimum
From first looks...
Looks like battery bank should be two 12 volts in series for 24 volts, and 3 parallel strings.
Also your AC and DC wiring is not well defined. Does the generator AC go to both inverters?
The inverter on the right has red and black wires labelled AC out.
Each inverter will draw over 100 amps DC at full load, one 80 amp fuse at the battery isn't gonna cut it.
Those 24v pip MPP units can only handle 2000w each. In your diagram each one would be pushing 2400w. The amp rating of MPPT is the output, not the input amps.
So considering that constraint, I would put 6 panels in series, so that it will create 132v, and 1800w for each MPPT.
Yeah that fuse needs to be much larger. Especially for surge. I would try a 250 amp fuse. Depending on your loadsFrom first looks...
Looks like battery bank should be two 12 volts in series for 24 volts, and 3 parallel strings.
Also your AC and DC wiring is not well defined. Does the generator AC go to both inverters?
The inverter on the right has red and black wires labelled AC out.
Each inverter will draw over 100 amps DC at full load, one 80 amp fuse at the battery isn't gonna cut it.
Yeah that fuse needs to be much larger. Especially for surge. I would try a 250 amp fuse. Depending on your loads
Also ensure that the wire size is large enough to handle tripping that fuse.
I edited my last comment. Be sure to check the update
FYI, Generators use fuel just to run themselves, they are typically most efficient when running at full load. Running it at full load for 4 hours will be more fuel efficient than running it at half load for 8.Good question on the AC in from the generator. I would think that my current needs only require it going to a single inverter but I'll have to review the docs on the parallel kit.
@evilvillain which program you used to draw this diagram ?I'm working on a design for a small off-grid solar system for a garage and put together the diagram below. I was hoping to get some feedback on whether this is valid or not from a high-level perspective. Thanks!
IView attachment 215
@evilvillain which program you used to draw this diagram ?
thanks !
Lovely diagram!
Some considerations:
Good luck with your system!
- Check your power losses. You're going to burning through at least 150W (P(loss) = I²R, therefore P(loss) = 17.2² x 0.64mΩ x 40 feet = 75W x 2 Arrays = 150W) just between the panels and the PV Disconnect. I'm guessing 250 - 300W losses in your PV system?
- I generally don't recommend fusing PV arrays, unless they are large. This one falls into that category. You need to protect from 'backfeeding' panels on short-circuit faults.
- Don't forget your PV bonding and earthing. All exposed metal needs to be bonded then earthed via your AC system ground conductor / utility provided earth.
- A 2 x 2,400 inverter would draw 100A +25% from your 48V battery.
- 4AWG cable is only rated for 120A (according to here), therefore this cable is under-specified for your intended use.
- That 120A rated cable is being protected by a 250A fuse, which is under-rated for your intended use.
- The potentially irregular cable run distances from your battery disconnect might cause irregular charging/discharging. See this article for more.
Personally, I would ignore all intra-device fuses - they are there to protect the device. You should be fusing the cables that connect the devices.The 250A fuses are built into the each of the BYD battery banks. With the batteries in parallel, do you think these fuses would be sufficient?
Most people tend to use WEEB-style bonding these days, rather than one contiguous cable. At least consider them.Grounding / Bonding - I need to add that to the PV panels. I have the wire for it, just forgot to add it to the diagram.
No, you just need to up the PV cable size ... or accept the losses, of course.In regards to power losses, I'm not sure how I could reduce this too much. I may be able to put the PV Disconnect in the middle of the array saving about 1/2 the distance.