I have 3 units installed and all 6 strings almost max out but im clipping at140 amps! And all three bypass to grid if load goes over 6000 watts. Tech support is buzy.
Right....but im only getting 140 amps across all inverters together. It is clipping output and pv charge at 140140 amps is the maximum charge current (Utility + Solar) on the 6000xp. See setting 6 on the LCD screen.
Right....but im only getting 140 amps across all inverters together. It is clipping output and pv charge at 140
But does that setting control all 3?THats just the master
Clipping all day at 3000 wattsCant go any higher ......they all are set to 140
Yes, it must be.Got to be a setting
Hmmm - the printed manual under Parallel Settings on page 23 says "Charge Current Limit (Adc): The maximum charge current limitation of the entire system in DC Amps.", which implies the limitation for the whole set. The Charge Current Limit(Adc) field on the EG4 portal shows "[0, 140/4480]" as the available range, which seems like you should be able to set 3*140 (420) on the master and that would be for the whole set. Weird it won't let you configure it for more than that.But does that setting control all 3?
I don't know, if they can be set individually. Or if they act as one.
Yes ill look again....but its in lead acid right now because im dealing with commHmmm - the printed manual under Parallel Settings on page 23 says "Charge Current Limit (Adc): The maximum charge current limitation of the entire system in DC Amps.", which implies the limitation for the whole set. The Charge Current Limit(Adc) field on the EG4 portal shows "[0, 140/4480]" as the available range, which seems like you should be able to set 3*140 (420) on the master and that would be for the whole set. Weird it won't let you configure it for more than that.
BTW - it also references a "Battery Shared" setting that should be enabled if they are all connected to the same battery bank. @parkerd I assume you have them all connected in parallel to the same bank and that setting is enabled...