8% voltage drop and running 80amps in 4 AWG for 300'
ddxv
Willits, California
I have panels that at a maximum would be max 67amps and 80amps including bifacial. The Ampacity chart shows that 80 is a bit close to 75c. Additionally, my calculation is that I would see 10.09v 8% voltage loss across the 300 feet from panels to Midnite Solar Classic 250 MPPT charge controller/batteries.
Setup:
8 old panels:
Watts: 295
Vmp: 36.5
Volts in Series: 146
16 new panels:
Watts: 440, bifacial 550
Vmp: 34.71
Volts in Series: 138.84
NameStringsSeriesPanel CountVMPPVolts From Panels
old panels24836.5146
new panels441634.71138.84
The total at source:
Old panels amps: 16
New Panels amps: 50 (normal) 63 (+bifacial)
Total amps: 66, 80 (+bifacial)
New panels spec sheet if needed:
https://signaturesolar.com/aptos-44...to-550w-with-bifacial-gain-dna-120-bf10-440w/
Setup:
8 old panels:
Watts: 295
Vmp: 36.5
16 new panels:
Vmp: 34.71
Old panels amps: 16
How many panels in series in a string?
Why not more in series and solve all your problems?
Right, currently both are in groups of 4 and I would also prefer to increase the voltage.
The first logical reason I had trouble with that 4 of the old panels are up on a tall pole mount, my uneducated assumption was that with 4 up in a group, I couldn't include those 4 in a series with other panels on a rack nearby since the panels (eg 4 on the pole, 2 somewhere nearby) would have an uneven gap in wiring going down the pole, underground, then back up into the main rack and thus would not work. What do you think?
The second less logical reason, ie, just ignore the pole, buy just new panels and put them in a longer series with 200v was that my mother (who's house is off grid) would not like to 'throw away' the old panels. 😅
Voltage drop doesn't hurt wild PV circuits, it's lost energy but the panels and controller won't mind. So as long as the wire is rated for it then it's acceptable.
What wire do you have out to the array right now?
If you up the voltage, don't do it by a little bit, get a 600v charge controller and run 8 in series. It's ok to have a long wire in the middle of a string, but a series string mostly doesn't benefit from part of the string being in better illumination, so not worth it to use the pole if you go with high voltage.
AWG 4, and I think THW or THWN-2/THHN. Since I wasn't sure which, I was assuming it's the lower THW for rating.
You've got 4 in place already? Well then yeah you don't have to switch you could stay with 150v.
Yes 4 AWG is good for 300 ft if stay under the current rating. I would do 2 strings of 8 to increase the voltage per string if the equipment will accept it and you can physically wire it that way.
No need for all new panels. You could simply add a charge controller for all the new panels and run wire for it, most likely much smaller AWG than 4AWG if you series the panels. Higher VOC rated charge controllers are fairly cheap.
What I would do? Leave that system in place, add a new mount and panels with that array having it's own charge controller.
One can never have too much array. :)
Get string voltage up, amps down is always my motto. I'm going to add that to my signature.
I also recommend getting the voltage up.
The power lost due to the resistance of the cable at maximum current of 80A is 960W.
Are you willing to give up the output of a couple panels when the sun is really beating down?
Just to heat up the wire in the ground?
Math
4 AWG copper: 0.25 milliohms per foot
600 feet total cable run (both + and -)
Power lost = I^2R = (80)(80)(0.00025)(600) = 960W
I don’t see a way around it, at least 8 in series. More voltage and different charge controllers. Factor in what your cold weather open circuit voltage is to help select the new charge controller(s).
Math
All three of you have the same recommendation, voltage up and amperage down. Is it possible to do with 4 panels on the pole mount and the remaining 20 in 3 strings of 8 in series nearby? The issue is that one string would have 4 panels on the pole mount, 30' wires, then the rest of the 4 in series.
Yes if all the panels on the strings are of the same model. I don’t know about the disconnect or safety issues that adds.
You might want to sketch that out for us just to be clear.
It's possible but not worth it. Giving 4 out of 8 panels in an 8 panel string better illumination just creates a shading condition, it will be more work and barely any better than 8 on the ground.
If you want to keep the pole, leave the 4S system in place with their charge controller as is, and build your new 8S system separately with it's own charge controller.
But this does mean running new additional wire from battery to array for the new separate system.
I started out with 4 panels per string with my first inverter which brought my voltage around 196v. After I changed over to the next inverter I tried 8 per string bringing my voltage up to around 300v. I noticed much better over all charging times as well as good starting voltage before the sun barred down onto the panels. Raise the voltage and bring the amps down is a smart move proved me.
Apologies, I'm not currently at my parents home where this is going to be done, so can't get a more straight forward pic. Panels in field, dog for scale ;). Combiner box in middle of panels goes to where picture is taken from, buried 4 AWG.
This is the current setup. Currently there are 8 panels in 2 strings of 4. The 4 on the left pole and the 4 in the two very DIY racks. The upcoming plan will be to take apart the old racks, which I made 15 years ago, and this time go with a solar specific rack. The new one supports 30 panels, if we want to expand in the future.
The new rack will be 4 old panels + 16 new ones. Most likely in the same spot as the 2 DIY racks.
So, when you suggested 3 strings of 8, it would work pretty well, as long as those 4 panels on the pole + 4 panels on a new rack immediately to the right could still be put together in series OK despite the gap, which since it would go down underground and across then back up, I guess is like 30 feet?
For reference, here is the comparison:
6 strings, 4 in series
NameStringsSeriesCountVMPPVolts From PanelsWattsMax WattsAmps by Lowest Voltage
old panels24836.5146295236016.99
new panels441634.71138.84440704050.70
Total Watts9400
Total Amps33.85
Volts to House277.68
Total Amps33.85
Dropped Volts to house5.05
Actual Watts at House?9229
Cost per Watt$0.80
3 strings, 8 in series
old panels18836.529229523608.50
new panels281634.71277.68440704025.35
Total Watts9400
Total Amps67.70
Volts to House138.84
Total Amps67.70
Dropped Volts to house10.09
Actual Watts at House?8717
Cost per Watt$0.85
Actually, I went a bit quick above the 3 series of 8 is in fact too high of voltage for the current Midnite Classic 250 MPPT Charge Controller, though I could do several strings of 6:
old panels16636.521929517708.50
new panels361834.71208.26440792038.03
Total Watts9400
Total Amps33.85
Total Amps33.85
Cost per Watt$0.80
Total Watts9400
Total Amps67.70
Total Amps67.70
Cost per Watt$0.85
Lucky SOB to wake up to a view like that every morning! My dreams. I even like the dog😂
I would be looking at a 600v controller to put all 16 in series. or as many as possible.
You can't have 3 series strings of mixed panel types and run them all over 2 4 awg wires.
My advice is just to scrap your old panels and go all new 8S2P over the existing 4 awg.
Otherwise, easiest to leave your old panels as they are on your old CC then run conduit and new wire to your new array and new CC.
Your VMPP is important, but also look at your OCV. If you add that value up in series, factor in cold panel voltage increase and if it’s higher than your max of your charge controller OCV rating, it’ll get expensive. The first day that those conditions are exceeded and your battery is fully charged with nothing to hold the voltage down, poof! The charge controller makes magic smoke.
You just need more wires. I don’t think many mppt can handle 10,000 watts.
You need to be able to bring multiple strings back to the multiple mppt you need for a higher power installation