I just want reliable panels are theSure is, paying for the RENOGY name.
I just want reliable panels are theSure is, paying for the RENOGY name.
I do not know about that brand, need to do research, my panels (4) are used SUNPOWER panels, SPR-230 at $70 each at my local pickup in North Bay.I just want reliable panels are the
Seraphim 305W a good panel
do I need a combiner box with a 3s2p setupI have used 250w Trina panels, but I wouldn't hesitate to buy these.
so if I get combiner I don't need inline fuses or do both?Need, no. Want, probably. You can use a MC4 two into one connector, but you still want to either run a 15a inline fuse on each branch or run them into a combiner box with breakers.
You should have fuse for each string.so if I get combiner I don't need inline fuses or do both?
it's going on a bus roofYou can do fuses or breakers (or both if you want). I have a Midnight Solar MPV6 combiner box with three 15a breakers. Some people recommend fuses because they are not polar (work in either direction), but I am ok with breakers only.
What are you putting this setup on? How much real estate do you have for panels? And it is this totally off grid? Tough to recommend gear without knowing the application.
frig a/c part time when somewhere hot led lights inside toaster oven occasionally tv/ ps4 few hrs maybe a desktop compI think I would just run inline fuses for cost, but a combiner box is nice if you have the budget. You can shut off each string if you have to work on it, and you can also test the output of each string by turning the other one off. So the panels are 65"x39". Not sure how much room you have on the roof, but I am thinking you can probably squeeze two side by side by three long. That would be about 6.5'x16.25'.
What are you trying to power?
I assume is 13.5 or 63Did you find out yet as to what the start up current (compressor kicks on) of the AC is yet? You do not want to get a surpise fInding out that Growatt cannot start up the AC.
Growatt spec show 6000VA surge capability but does not say for how long.
Lock Rotor Amp (LRA) OF 63A, so 120VAC * 63A = 7560VA since it is inductive load.I assume is 13.5 or 63
so it won't run the a/c?Lock Rotor Amp (LRA) OF 63A, so 120VAC * 63A = 7560W
I do not know if the Growatt can handle it or not, and I hope it has good protection so it will not blow up incase of overload.so it won't run the a/c?
Solar is just another alternate power source, even with other power sources,I.E. Utility, Generator, you still have to find out if it can handle the load or not.I hate this whole process of figuring out solar
I have a hard time believing a 13k btu AC will pull 7500 watts at start up. That sounds really high unless this unit is very old. Most 12-13K AC units pull less than 3000 watts at start up.