They are wired half series half parallel.
Thanks
‘Overloading’ implies your Epever SCC is under strain and could eventually suffer damage or premature death.
The answer to that question is ‘NO’, your 50A Epever SCC should have no difficulty handling your 6x280W panels.
‘Overpanelling’ means that you have enough solar power wring your Epever SCC that it can cause clipping during the peak part f the day, and the answer to that is ‘yes, depending on battery voltage.’
If you are charging a 24V battery, 50A x 24V = 1200W.
You have 6x280W = 1680W of panels capable of putting out well over 1200W of solar power under the right conditions.
When that happens, your SCC will limit charge power to 50A / 1200W, so you will be ‘clipping’ potential solar charge power that will be wasted.
If you are charging a 48V battery, your same SCC will not clip below 50A x 48V = 2400W, so your SCC will never be forced to clip incoming solar power from your 1680W solar array.
Typical solar arrays rarely exceed ~90% of ratings during summer months and even less through the rest of the year, so in practice, you 1680W array is rarely going to give you over 1500W of power meaning you’ll never be clipping more that 20% of your potential power when charging a 24V battery at midday over summer months.