I think it still applies when the conduit transitions to the building. That part is "in a building". As soon as you come up the wall or through the foundation, you need to have metal conduit. You read it the same way I do for ground mount - you can do PVC until you get to that building.690.31(D)'s paragraph title says "on or in a building" but the text only talks about "in" a building. It would appear to me that the "on" part only refers to roof mount systems. Mine will be a ground mount.
It would not apply if your ground mount array and inverter are all outdoors not inside a structure.
Looks like it wasn't required -> required in 2020 -> exempted in 2023.RSD - I thought that I had this one packed away a long time ago. Thought that I had read somewhere that ground mount systems did NOT require RSD. I've read 690.12 and that text is as clear as mud to me. Am I correct in believing for a ground mount array that an RSD is not required?
As of 2023 NEC:
"Ground-mounted PV system circuits that enter buildings, of which the sole purpose is to house PV system equipment, shall not be required to comply with 690.12."
That exception didn't exist in 2020 NEC. Here, they wouldn't pass that - they don't honor the newer code.
Ask who is doing the inspection. I believe NEC requires the disconnect to be on the "building" (not at the array) or inside at the point of entry. I am NOT CLEAR on this, so you want to comply with who is going to be checking off on the permitting. Here, they want it on the building and require that it's outside. Needs an obvious label. Basically they want to make it super easy for firemen to find.In any case I plan on including a manual disconnect at the array. And then the SolArk has a PV disconnect switch on it and the PV wire enters the wall less than 3' from the SolArk. So I think I'm covered on the disconnect requirement?
Same situation here, except there is no "state inspection". It's the POC inspection only (it's their grid, no state grid). It's worth having a conversation with the inspection (state) over having to re-wire something.The rural co-op rep told me that they have their own inspection criteria. He said that if the state passed the installation, that MOST LIKELY they would also pass it. I live in a rural, technically backwards county. I'd classify them as at least 10 years behind other places. The rural co-op does not like residential solar, but need the offsets for the state. They are into commercial solar that they then resell to the consumer. This has been an uphill battle. For the county inspector, I had to show proof that LFP batteries were relatively safe, did not require a vented cabinet and did not require a drain.
Way better to figure it out, draw it out, than have surprises. You're doing just fine. This crap is complicated and it changes.I had thought that I had reduced my list of issues/questions to just figuring out how to interface with the grid: gutter sizes, types of splices or power distribution blocks, wall pass throughs, most efficient way to wire the xfer switch and production meter, conduit fill, EGC, etc. But I think I'm doing a circle back on things I thought I had understood.