hpeyerl
- Mar 22, 2022
- 58
Starting a new thread because I created confusion by hijacking this thread: https://diysolarforum.com/threads/n-g-bonding.80429
In that thread I posted photos of my meter set-up: https://diysolarforum.com/threads/n-g-bonding.80429/post-1032841 I apologize for creating confusion.
A few folks responded with questions which I'll try to answer here and hopefully un-hijack that other thread..
This is the way the power-company directed the install. Maybe this is the part where I mention I'm in Canada but I thought the CEC largely mirrored the NEC. I previously had overhead power from the pole to the house and due to some renos, switched to underground from the pole to the house. The PowerCo said I should trench it myself, drop in some 4/0 USEB-90. They came out when I was done and rebuilt the meter base as you see in the photos. The house has its own ground plate. The other line in the photo was pre-existing 2AWG USEB-90 to the shop. The shop has its own dual rod ground setup.
So this is the way it is currently configured but I was confused about the conflicting information from various electricians/inspectors. What you describe is what my intuition says is correct.
That was how the power-co spec'd it. The cable on the right was existing; and the cable on the left was USEB-90 which the power-company told me to run to my house when I switched from overhead. They upgraded the meter base and did all that wiring in the box.@Mattb4
ETA: Incidentally I have never seen it allowed to use bare wire as a Neutral feed like you have from your pole panel. Where I am at I had to run 4 wires with one being the bare ground.
Yes it is. I guess that's the bonding.@B-Mod
Is the bar on the right directly bolted to the enclosure, or is it isolated? Can't tell by picture.
@timselectric
And there should be 4 conductors to each building, if done correctly. (L1, L2, N, G)
And no other N/G bonds.
@wheisenburg
Without knowing your exact setup, it is hard to say for sure. I can tell you that as a general rule, separate buildings will have separate electrical systems. They should only be supplying three wires to each building. Two hots and a neutral. At the entrance to each building you should have ground rods installed and tied into the panel at each building. That is where the ground neutral bond should be established.