Yes, I plugged in the panel specs to the form and it was ok. Then I ran the high end extra output I had just gotten and it was still was ok. It looked like too many amps though so I called Midnight Solar and they affirmed it but said I should go from my 80 amp breaker to a 100amp or my charge controller could cause they also said the unit will clip some of the power off if needed so the controller can be over paneled and hold up::::)))))))I read the result wrong. 2s 2p works fine for 4 x 445 watt panels.
Classic Sizing Tool
PV Module DataPower 445 Watts VOC 48.9 Volts VMP 40.9 Volts ISC 11.54 Amps IMP 10.89 Amps VOC Temp Coef % 0.33 C VMP Temp Coef % 0.45 Amps Environmental DataColdest Ambient Temperature -22 F Hottest Ambient Temperature 104 F Nominal Battery Volts 24 Volts PV ArrayNumber Of Modules In Series 2 Number Of Parallel Strings 2 Total Modules 4 Rated PV Array Power 1780 Watts Anticipated Array Power @ 104 F 1660 Watts Rated PV Array Current 21.78 Amps Battery Charging Current @ 28.8V 61.8 Amps VMP (Maximum Power Point Voltage 81.8 Volts VOC (Open Circuit Voltage) 97.8 Volts VMP @ -22 F 102 Volts VOC @ -22 F 115.6 Volts Charge ControllersCLASSIC 150/LITE CLASSIC 200/LITE CLASSIC 250/LITE
NOTE: MidNite Solar recommends a second controller be added after 1.2
Max Operating Voltage 150 200250 Max None Operating VOC (HyperVOC) @ 48V Nominal Bat Voltage 174 224274 Maximum Number Of Modules In Series Configuration 2 34 Max Number Of Modules In Series Using HyperVOC 3 34 Max Allowable Output Current Per Classic Based On This Current 94 7462 Max Allowable Wattage Per Classic Based On This Configuration 2700 21231779 Present PV Array Wattage Of This Configuration 1780 17801780 Design CheckMax VOC OK OKOK Temp The Classic Enters HyperVOC -214.6 F° -493.6 F°-772.6 F° Array Power (Wattage) OK OKEXCESSIVE Classics Required 0.7 0.91.1
WARNING: MidNite Solar makes no representation, warranty or assumption of liability regarding the use of the String Calculator. This tool uses data provided by other parties (such as PV module specs) and makes calculations based on assumptions which may or may not prove to be valid.
I am thankful that you and others got me to look more closely at it and learn much more!
I’m good to go?