I read the result wrong. 2s 2p works fine for 4 x 445 watt panels.


Classic Sizing Tool

PV Module Data
Power445Watts
VOC48.9Volts
VMP40.9Volts
ISC11.54Amps
IMP10.89Amps
VOC Temp Coef %0.33C
VMP Temp Coef %0.45Amps
Environmental Data
Coldest Ambient Temperature-22F
Hottest Ambient Temperature104F
Nominal Battery Volts24Volts
PV Array
Number Of Modules In Series2
Number Of Parallel Strings2
Total Modules4
Rated PV Array Power1780Watts
Anticipated Array Power @ 104 F1660Watts
Rated PV Array Current21.78Amps
Battery Charging Current @ 28.8V61.8Amps
VMP (Maximum Power Point Voltage81.8Volts
VOC (Open Circuit Voltage)97.8Volts
VMP @ -22 F102Volts
VOC @ -22 F115.6Volts
Charge Controllers
CLASSIC 150/LITE CLASSIC 200/LITE CLASSIC 250/LITE

Max Operating Voltage
150​
200​
250
Max None Operating VOC (HyperVOC) @ 48V Nominal Bat Voltage
174​
224​
274
Maximum Number Of Modules In Series Configuration
2​
3​
4
Max Number Of Modules In Series Using HyperVOC
3​
3​
4
Max Allowable Output Current Per Classic Based On This Current
94​
74​
62
Max Allowable Wattage Per Classic Based On This Configuration
2700​
2123​
1779
Present PV Array Wattage Of This Configuration
1780​
1780​
1780
Design Check
Max VOCOK
OK
OK
Temp The Classic Enters HyperVOC-214.6 F°
-493.6 F°​
-772.6 F°
Array Power (Wattage)OK
OK
EXCESSIVE
Classics Required0.7
0.9
1.1
NOTE: MidNite Solar recommends a second controller be added after 1.2

WARNING: MidNite Solar makes no representation, warranty or assumption of liability regarding the use of the String Calculator. This tool uses data provided by other parties (such as PV module specs) and makes calculations based on assumptions which may or may not prove to be valid.







Yes, I plugged in the panel specs to the form and it was ok. Then I ran the high end extra output I had just gotten and it was still was ok. It looked like too many amps though so I called Midnight Solar and they affirmed it but said I should go from my 80 amp breaker to a 100amp or my charge controller could cause they also said the unit will clip some of the power off if needed so the controller can be over paneled and hold up:::::))))))))
I am thankful that you and others got me to look more closely at it and learn much more!
I’m good to go?
 