I have 2 Sunpower flexible 170W panels. Can't use in series, because of the system voltage limit of THE PANEL!
Their rated current is 5.84 A so in parallel I risk 11.68A at the 10 A limited input to the Bluetti EB240.
Should I risk that Bluetti's input A is as conservatively rated as their input V?
Look for some current-limiting device that won't kick in 'til 10A ....Oh, wait... that's a fuse ,
Perhaps an easy-access fuse and hope that the panels never, or rarely enough ever put out 11.68 A?
or just use the one panel and get an AC200 in a month or two & let you guys have this one at a great price?
Will pose the same question in panels/connection.