Sorry I read your post wrong...I do have a breaker between the eg4 and the SE.
You let me know what you want me to test and I can test it for you this weekend.
I'm already testing 8s vs 4s2p and the results are underwhelming... So I need a new thing to play with
What was underwhelming about it?
Hmm, I'd like to see how stable the AC output is when used solely as an AC battery. IE, when the 18kpv is grid forming and has no choice but to alternate between absorbing AC output from the SE and inverting from the battery.
So:
- DC solar disconnected (remember to do this with zero load, not sure how to do this on this inverter). If the solar is connected then it may give help to the high voltage DC bus, I think this is why SolArk requires some DC.
- Voltage monitoring on AC output (critical loads panel voltage)
- Power monitoring on SE circuit and 18kpv AC output. To see who is sending power when.
- Disconnected from grid
Experiment one:
- Start with zero load. Have a load ready to go that is high enough to exceed AC from microinverters.
- Flip loads on and off, with the loads just high enough to exceed the AC output from the microinverters. This will require the inverter to either switch back and forth between charging and inverting, OR turn off the AC coupled power.
- One way to do this automatically would be to set a dryer on the appropriate cycle, and toss some moist stuff in it. As the stuff dries, it will reduce the duty cycle. On mine it just goes full blast into 5 kW. However this will only test 240V
Experiment two:
- Start with load just below AC output of microinverter
- Cut microinverter when load is on. This will require the inverter to kick in
- Turn microinverter on, see how well inverter manages the rampup while off grid (probably fine and not interesting, it's slow)
It would be interesting to see the behavior for 120V vs 240V loads, since 120V loads still need some help from the inverter to handle neutral current, but that would be getting greedy :laugh: