I love AC coupling with a passion: it's super cheap for the amount of pv you can connect, you take the load off your main inverter during the day, it's highly efficient at running loads, and it gets MORE efficient at high output- when my pv inverter is absolutely running 100% flat out the efficiency is 98%.
A battery inverter running flat out would be in the 80s for efficiency probably.
But, charging a battery from ac coupled pv is not very efficient. You have the losses from the pv inverter, plus losses in the battery inverter converting ac to DC again- I have seen as low as 84% !
So, maybe the answer is having some pv on a DC coupled charge controller? I did that recently and it's pretty nice I must say! I can have the ac coupled pv only run loads or export to the grid at high efficiency, and at the same time charge the battery at 98+ percent efficiency from the DC coupled charge controller.
Btw, victron os is the shiznit!
A battery inverter running flat out would be in the 80s for efficiency probably.
But, charging a battery from ac coupled pv is not very efficient. You have the losses from the pv inverter, plus losses in the battery inverter converting ac to DC again- I have seen as low as 84% !
So, maybe the answer is having some pv on a DC coupled charge controller? I did that recently and it's pretty nice I must say! I can have the ac coupled pv only run loads or export to the grid at high efficiency, and at the same time charge the battery at 98+ percent efficiency from the DC coupled charge controller.
Btw, victron os is the shiznit!