daklein
New Member
- Joined
- May 8, 2020
- Messages
- 190
I recently finished a DIY transfer switch box to move my grid tied array between the grid and the island/off-grid panels. It is a 4.7kw 'grid-tied' system with microinverters which goes through a generation meter. The motivation is to use the grid-tie system energy in the house directly where possible and when there is very little credit for outflow, but still be able to send it out during weekday peak rates if I can't use it. The 'off-grid' is the island AC1 side of a pair of SMA SI6048 inverters & batteries, in the garage at the far end of the house, with about 7kw of AC and DC coupled solar with FLA forklift batteries (DC Solar trailer parts).
The transfer switch contactors move L1&L2 to backfeed either the grid panel (to the right outside) or off-grid panel (basement). The contactors are 30a (20a continuous) rated, and I swapped out the position sensing 4th contact hardware, so they're 4 poles at 20a, 2 for each L1&L2. The array can potentially put out around 20a.
The transfer switch runs on timers as a default, to connect to the grid during on-peak rates. I set the timers manually if I want to keep the extra solar on the off-grid side; on cloudy days I can use all the solar in the house. In the future, I'll have the other system controls run this also, via a set of 24v dc inputs that override the timers.
The relays and timers run on 24v DC, powered from the off-grid side. In addition to the mechanical interlock between the contactors, the control relays are also wired to prevent energizing both contactors at the same time. If the timers or the override control inputs attempt to enable both contactors, then neither contactor energizes.
Here are pictures of the transfer switch: https://photos.app.goo.gl/UcDfekbC1J3qAJ6J9
The transfer switch contactors move L1&L2 to backfeed either the grid panel (to the right outside) or off-grid panel (basement). The contactors are 30a (20a continuous) rated, and I swapped out the position sensing 4th contact hardware, so they're 4 poles at 20a, 2 for each L1&L2. The array can potentially put out around 20a.
The transfer switch runs on timers as a default, to connect to the grid during on-peak rates. I set the timers manually if I want to keep the extra solar on the off-grid side; on cloudy days I can use all the solar in the house. In the future, I'll have the other system controls run this also, via a set of 24v dc inputs that override the timers.
The relays and timers run on 24v DC, powered from the off-grid side. In addition to the mechanical interlock between the contactors, the control relays are also wired to prevent energizing both contactors at the same time. If the timers or the override control inputs attempt to enable both contactors, then neither contactor energizes.
Here are pictures of the transfer switch: https://photos.app.goo.gl/UcDfekbC1J3qAJ6J9