Copied from another thread.
So, we were having the same issue. I noticed the yellow arrows were feeding power to the EPS rather than standard consumption. I'm not sure what the EPS stands for but by reading what I did it was meant to be hooked up to a critical loads aka backup panel. Following the flow charts in the manual gets it set up this way.
What we did to fix it was turn OFF off grid mode. This moved the arrows to consumption mode rather than EPS. I don't know why EG4 labeled it the way it did, but EPS mode does not like very high inrush current. By switching this, we went from an 18kpv that wouldn't even start a 2 ton ac to one that would not only start the two ton, but start a 4 ton on an easy start with the 2 ton running and about 2k worth of normal loads.
I'm not sure how it'll work without grid connection but I would think it would do the same.
In brief, if your 18kpv won't start ac even with micro air soft start, turn OFF off grid mode.