Hi All,
My EG4 18K will power loads in EPS mode (backup power enabled). But, it won't power any loads in regular consumption mode. I have all my loads on a critical loads subpanel feed off the loads port on the 18K.
The problem is in EPS mode the 18K isn't running my new AC unit smoothly. I have a soft start on the AC unit, but in EPS mode, it sometimes lags on startup and if the AC turns on when the car is charging, the car will stop charging.
The AC only pulls 3500 watts once it's up and running.
When I'm in regular, consumption mode, it looks like the below picture where it'll actually curtail solar, and power the loads from the grid. The 2,300 watt load is the AC in stage 1.
Any ideas??