EG4 18Kpv strange occurrence

Bananaman321

⚡solar idiot ⚡
Joined
May 18, 2024
Messages
120
Location
Fairfax, SC
Eg4 18kpv luxpower, 2 wall mount batts 280ahr+ 4 eg4 lifepower4 server rack batteries, 2solar arrays 6 panel series and 12 panel series fed into #2 and #3 inputs 370w panels
Running off grid for over a week no problem 4500w water heater, 4000w+ well pump, and 4ton ac intermittently as a load dump bringing in more than I need.
Firmware update 2 days ago
So I'm grid tied but have had main disconnect between feeder tap and inverter off because when I initially brought it online it was still using some grid pwr so I left it this way till I could figure out right settings for "self consumption mode" the manual kinda jumps around and some of the terms didn't make sense I even downloaded the Luxpower 12k hybrid manual to compare
So anyways today batteries over 76% 4k+ solar coming in I turned on the 4ton ac and it seemed to struggle starting also lights were all flickering and when air handler kicked in it mad an odd grouling sound and flickering worsened so I turned ac switch to off and back to cool this gave me 3 min to get downstairs to monitor inverter when compressor kicks in watching the interface "no faults or alarms recorded" could not see a change on display hred slight buzz as compressor attempts to start 0.5-1.5 seconds nostart it (unit has defrost board and sensitive to power fluctuations it is also like 18yrs old) so I proceeded outside for next attempt and almost instantly kicks out this time. So I turn on main disconnect to inverter and proceeded inside and restart inverter now while on grid bypass for (300sec. default) the ac starts right up and seamlessly transfers to inverted power after elapsed time and has been running ever since.
I will update with some screen shots of display settings and firmware I took after reset
They are on my phone that's why not in this post
This is all brand new equipment from Signature Solar if one of team members wants to login and check it out its online and I'm game for that 20240607_182259.jpg20240607_182315.jpg20240607_182328.jpg20240607_182341.jpg20240607_182358.jpg20240607_182412.jpg20240607_182424.jpg20240607_182445.jpg20240607_182506.jpg20240607_182521.jpg
 

Attachments

  • Screenshot_20240607-183049_EG4 Monitor.jpg
    Screenshot_20240607-183049_EG4 Monitor.jpg
    74.3 KB · Views: 13
Last edited:
Eg4 18kpv luxpower, 2 wall mount batts 280ahr+ 4 eg4 lifepower4 server rack batteries, 2solar arrays 6 panel series and 12 panel series fed into #2 and #3 inputs 370w panels
Running off grid for over a week no problem 4500w water heater, 4000w+ well pump, and 4ton ac intermittently as a load dump bringing in more than I need.
Firmware update 2 days ago
So I'm grid tied but have had main disconnect between feeder tap and inverter off because when I initially brought it online it was still using some grid pwr so I left it this way till I could figure out right settings for "self consumption mode" the manual kinda jumps around and some of the terms didn't make sense I even downloaded the Luxpower 12k hybrid manual to compare
So anyways today batteries over 76% 4k+ solar coming in I turned on the 4ton ac and it seemed to struggle starting also lights were all flickering and when air handler kicked in it mad an odd grouling sound and flickering worsened so I turned ac switch to off and back to cool this gave me 3 min to get downstairs to monitor inverter when compressor kicks in watching the interface "no faults or alarms recorded" could not see a change on display hred slight buzz as compressor attempts to start 0.5-1.5 seconds nostart it (unit has defrost board and sensitive to power fluctuations it is also like 18yrs old) so I proceeded outside for next attempt and almost instantly kicks out this time. So I turn on main disconnect to inverter and proceeded inside and restart inverter now while on grid bypass for (300sec. default) the ac starts right up and seamlessly transfers to inverted power after elapsed time and has been running ever since.
I will update with some screen shots of display settings and firmware I took after reset
They are on my phone that's why not in this post
This is all brand new equipment from Signature Solar if one of team members wants to login and check it out its online and I'm game for that View attachment 220489View attachment 220490View attachment 220494View attachment 220495View attachment 220496View attachment 220497View attachment 220498View attachment 220499View attachment 220500View attachment 220501
Can’t help you with the 18KPV settings but might want to consider a Microair soft starter to limit those LRA of your compressor.

You will need to select the size necessary for your unit.

 
Eg4 18kpv luxpower, 2 wall mount batts 280ahr+ 4 eg4 lifepower4 server rack batteries, 2solar arrays 6 panel series and 12 panel series fed into #2 and #3 inputs 370w panels
Running off grid for over a week no problem 4500w water heater, 4000w+ well pump, and 4ton ac intermittently as a load dump bringing in more than I need.
Firmware update 2 days ago
So I'm grid tied but have had main disconnect between feeder tap and inverter off because when I initially brought it online it was still using some grid pwr so I left it this way till I could figure out right settings for "self consumption mode" the manual kinda jumps around and some of the terms didn't make sense I even downloaded the Luxpower 12k hybrid manual to compare
So anyways today batteries over 76% 4k+ solar coming in I turned on the 4ton ac and it seemed to struggle starting also lights were all flickering and when air handler kicked in it mad an odd grouling sound and flickering worsened so I turned ac switch to off and back to cool this gave me 3 min to get downstairs to monitor inverter when compressor kicks in watching the interface "no faults or alarms recorded" could not see a change on display hred slight buzz as compressor attempts to start 0.5-1.5 seconds nostart it (unit has defrost board and sensitive to power fluctuations it is also like 18yrs old) so I proceeded outside for next attempt and almost instantly kicks out this time. So I turn on main disconnect to inverter and proceeded inside and restart inverter now while on grid bypass for (300sec. default) the ac starts right up and seamlessly transfers to inverted power after elapsed time and has been running ever since.
I will update with some screen shots of display settings and firmware I took after reset
They are on my phone that's why not in this post
This is all brand new equipment from Signature Solar if one of team members wants to login and check it out its online and I'm game for that View attachment 220489View attachment 220490View attachment 220494View attachment 220495View attachment 220496View attachment 220497View attachment 220498View attachment 220499View attachment 220500View attachment 220501
 
n4ton ac intermittently as a load dump bringing in more than I need.
So anyways today batteries over 76% 4k+ solar coming in I turned on the 4ton ac and it seemed to struggle starting also lights were all flickering and when air handler kicked in it mad an odd grouling sound and flickering worsened so I turned ac switch to off and back to cool this gave me 3 min to get downstairs to monitor inverter when compressor kicks in watching the interface "no faults or alarms recorded" could not see a change on display hred slight buzz as compressor attempts to start 0.5-1.5 seconds nostart it (unit has defrost board and sensitive to power fluctuations it is also like 18yrs old) so I proceeded outside for next attempt and almost instantly kicks out this time.
A 4 ton normal AC can spike up to 105 amps. For me, this is 24 KW of surge and seems to last a second or two. Do you have a hard start or soft start attached? A soft start would be ideal.

Often, they have hard starts attached to it, so I don't know if this adds to it or subtracts from the startign load, but it dumps enough amps at it to get the motor going.

A Soft Start is better for these solar inverters and can start it slower and not need 105 amps to start it. I have an Outback inverter and when a soft start was added to another person's Outback this light flickering went away. My lights flicker and I've stopped running the 4 ton AC off the battery, but will after I get a soft start installed.
 
I just shut down and restarted ac no problem
As this has been the case every other time I've tried to start it
 
Last edited:
A 4 ton normal AC can spike up to 105 amps. For me, this is 24 KW of surge and seems to last a second or two. Do you have a hard start or soft start attached? A soft start would be ideal.

Often, they have hard starts attached to it, so I don't know if this adds to it or subtracts from the startign load, but it dumps enough amps at it to get the motor going.

A Soft Start is better for these solar inverters and can start it slower and not need 105 amps to start it. I have an Outback inverter and when a soft start was added to another person's Outback this light flickering went away. My lights flicker and I've stopped running the 4 ton AC off the battery, but will after I get a soft start installed.
This ac unit has also started with other loads like water heater and other appliances going at the same time without a problem this is a one time occurrence
 
Last edited:
All seems fine now I'll update if it happens again still open to having EG4 tech check it out if they like
 
Other than this I love the unit it runs while my loads just as it should
Air compressors water heater welders well pump you name it

Amazing machine20240529_002412.jpg20240531_084629.jpg20240606_033219.jpg20240606_032956.jpg20240529_031618.jpg20240528_065017.jpg
 
Last edited:
As we've all seen on this forum there are many different ways to get to the same outcome
And that's why we are here to learn
I know I've learned a ton since in the short time I've been a member
And probably forgotten twice as much🤪

I'm not as smart as I seem nor as dumb as I look proceed with caution🙃
 
Last edited:
I've never been a part of any of these forum types things before so beer 🍺 with me while I catch up a try to figure out some of this technical crap.
 
Can’t help you with the 18KPV settings but might want to consider a Microair soft starter to limit those LRA of your compressor.
I concur.
I've got two 3-ton HVACs with the EasyStart 368, and the inverters don't even break a sweat.
A 4-ton unit will have super high LRA current, the abuse on the inverters every time it starts up should be avoided.
It's also not great for the compressor if it stalls due to brownout.
 
You are asking an awful lot of that inverter without a soft start. However what version of firmware did you go from and to?
 
I concur.
I've got two 3-ton HVACs with the EasyStart 368, and the inverters don't even break a sweat.
A 4-ton unit will have super high LRA current, the abuse on the inverters every time it starts up should be avoided.
I'm pretty sure my problem is not with the load but the firmware update I just installed
I've tested this unit with other equipment running without any problems
 
I'm pretty sure my problem is not with the load but the firmware update I just installed
I've tested this unit with other equipment running without any problems
Also I heard there was supposed to be 2 firmer updates at a time there only seemed to be one I didn't know if I should reinatate it or not
 
I'm pretty sure my problem is not with the load but the firmware update I just installed
I've tested this unit with other equipment running without any problems
It very well could be but what’s the harm in limiting the surge current?

$400 is pretty cheap insurance.
 
It very well could be but what’s the harm in limiting the surge current?

$400 is pretty cheap insurance.
I don't have to run this unit and it is soon to be replaced I have other means of climate control

Plus I don't see how throwing soft starts at large inductive loads is a reasonable solution to what seems to me to be a software issue

I have had no fluctuations with any other large inductive loads since restart

Maybe that's all I needed was a restart