rggsolardiyguy#2023
New Member
Hi I have 2 EG4 6000ex inverters connected together off grid only with no grid power. With 30 420 watt panels. Two String of panels. 16 panels in string 1 14 panels in string 2. Each String is at around 390volts 21amps. I have 12 300amph kilovault batteries 3 strings of 4 for a total of 900amph 48V 46K worth of storage. I got Inverter 1 wired PV in + - from pv string 1. Inverter 2 + - from pv string 2. with pv disconnects wired in between. For the batteries I have 2 bus bars one + one - with both + coming from each inverter and the - Bus bar wired with both - coming from each inverter with + &- coming from the batteries with DC disconnect breakers wired in between. For AC output Inverter 1 L1 L2 going to a Square D QO 60am breaker with N on the N busbar and grounds wired together. Inverter 2 is wired the same going to the other 60 amp breaker. Both Breakers back feed a 100 amp Square D QO indoor panel which feeds my main load panel. I have L1 L2 N legs wired back to my main loads panel from the main lugs on the ac combiner box. The problem I'm having is that when I run both inverters together I get a random power outage for 2-5 seconds then the power comes back on automatically with no fault codes or alarms going off. I then ran each inverter in solo mode and they worked fine with no issues. Thus I think its cant be a wiring problem because both inverters run fine when on there own. They only have the random power outage when I hook them back up to run together. I have done the firmware up date both inverters show Main cpu 06311 slave cpu 06108 firmware. Has anybody else had this problem? Are EG4's junk inverters should I return them back to Signature Solar ASAP? please help! I'm running out of options?