I think I heard someone mention that removal of that bond as being very important.Mine do not do that.
I have no grid connection.
1 inverter n/g bond in place, 2nd unit n/g removed.
MDP has isolated neutrals
Gen has n/g bond
"Gen mode". Do you have your generator connected to the AC input? If so what size wire are you using?. I would like to do that as well once I figure out the issues.Excellent info. I get back to you. Thanks
Very good to know thank you. One hot to each inverter and split the neutral I suppose. I have the same setup as you describe but on solar my voltage fluctuates wildly and I'm running out of things to try.Yes. The wire, breaker , disco, etc...will be sized based upon your generators output. Mine only provides 25 amps @240vac, so I have #10 wire and 30 amp breakers.
What is Signature Solar saying?Very good to know thank you. One hot to each inverter and split the neutral I suppose. I have the same setup as you describe but on solar my voltage fluctuates wildly and I'm running out of things to try.
It's been over two months, what happened?Well, I give up. I can run either inverter on either string of PV one at a time and the AC is steady at 120v. When I connect one inverter to PV, one runs off the battery correctly and one off of the connected PV, voltage is steady on both. I just can't run both inverters on PV at the same time without the outputs on both inverters fluctuating by 40 v or so up or down. Works fine on just batteries. Also strange is when testing PV wiring there are 34 volts coming OUT of the PV Input ports on each inverter, even when I completely disconnect the solar to both inverters I still read 34 volts at the inverter PV inputs. I can connect up the PV wires inside the house and go out where they connect to the panels and read 34v heading toward the panels. When I shut off the inverters that drops to 10v coming out of each inverter on the pv input lines.
No AC input and all breakers are off.
This is a good one.
Also, if I connect a 1500 watt 120v load, a heater running on solar the output is steady 120v.
@BenFromSignatureSolarIt's been over two months, what happened?
I just got my system running November 9th. I also have fluctuation issues. I've left the grounding screws in both inverters for now, concerned about warranty and Richard said it was tested that way. Have emails in to Aaron at SigSolar. @TheBestDIYGuy help.
set to 120, 2p1, 2p2 split phase 180,
When running with utility on the AC output on both inverters fluctuate between 119-121v.
When running on PV/Battery the AC output on the inverters fluctuates, a lot.
Inverter 1 is typically 110-112v when there is any load, if the load is just to run the inverter it is 119-121v.
Inverter 2 is typically 119-121v, but when the sun is going down and the PV is turning on and off the AC output jumps wildly from 114-123-119-121-112-120-114v etc. Attached here is that data, I also have video of the inverter screens:
View attachment 120118
Here is a screen of the data throughout the day showing the AC output fluctuations:
View attachment 120119
this is with grid on at about 1120, saved a day before the above graphs.
View attachment 120120
Split EG4 6500 AC Output varies
Split phase system started on 8th, Solar Assistant on the 10th. Is it normal to see AC output data showing inverters sometimes at 110-112V while the other inverter is at 119-120V? @BenFromSignatureSolardiysolarforum.com
I'm trying that as we speak. Just turned on the one "problem" inverter and changed output mode to Single. It's running the circuit just fine right now, but i'm not in there monitoring it constantly so i don't know if it has cut out at all. However, everytime i have checked it in the last few minutes it has been solid at 120v with no light flickering.Can you un parallel them and test them separately to see what happens? It seems to me like one of them is faulty. My pair of sp6548 in split phase have absolutely rock solid 120 volt output each.
I've done the single mode test before. Only in parallel do they have voltage problems.I'm trying that as we speak. Just turned on the one "problem" inverter and changed output mode to Single. It's running the circuit just fine right now, but i'm not in there monitoring it constantly so i don't know if it has cut out at all. However, everytime i have checked it in the last few minutes it has been solid at 120v with no light flickering.
What did Tier 2 tell you today?I've done the single mode test before. Only in parallel do they have voltage problems.