Good enough for me, thanks.
Sounds like a dead short to me, thanks.The test I did was using a roughly 24 inch 2/0 cable, connected directly to the battery terminals: Result - BMS turned off the power.
Bypassing the BMS with the same cable: Result - tripped breaker.
This would be some good YouTube content.The test I did was using a roughly 24 inch 2/0 cable, connected directly to the battery terminals: Result - BMS turned off the power.
Bypassing the BMS with the same cable: Result - tripped breaker.
Ya, I was going to get a video of the test but it was literally a "oh I'm walking by the workbench let me do this test people want real quick" moment and I'm in the middle of another larger project. I'll get a video on it asap though.This would be some good YouTube content.
Seriously.
Out of stock until mid May.$49.99 * 6 = $299.94TFB1-150, 150A Class T Fuse Kit | DonRowe.com
The TFB1-150 offers 150 amps of over-current protection and provides safe operation of your inverter.www.donrowe.com
Luckily the built-in breaker can quench a dead short.Out of stock until mid May.
Edit: fuses only. Full kits are available.
Texican, I too was looking for EG4 battery bank to work with LV6548. I spoke to watts247 who said EG4 not communicate with LV6548, and was recommended Pytes 5.1KW batteries; pretty slick how batteries connect in parallel with snapon cable clips. I also saw Will Prowse using SOK 5.1KW batteries with LV6548. I'm trying to decide which ones to get (Pytes or SOK), but really like EG4.Building a off grid / grid assist system with 2 LV6548 and a bank of 6 EG4 48v batts
using 48 used 250 watt panels. planning 6s2p for 3000 watts to each of the 4 mppt inputs 12kw total
I have a few questions on fuses etc
1. T fuses between inverters and batteries..should I be using 200 amp or 300 ?
2. I have 4 strings of panels, I need 4 dc breakers at 30 amps, what are a lot of you using for this ?
3. A/C input, the inverter manual seems to call for 4ga wire for AC input and output. how many amps are being fed in ? and how is it divided to serve both LV6548s ? separate breakers and wires to each inverter from the main panel ?? should I install a a/c disconnect for the ac input ?
4. what is a shunt ? and do I want or need one ? Ive seen smart shunt that sends battery info
thanks for any advise
Could you provide a link to these batteries?and was recommended Pytes 5.1KW batteries; pretty slick how batteries connect in parallel with snapon cable clips.
I am using solar assistamt for a brain on my system, still having issues with it seeing the eg4 bank, only sees 1 battery right now, solar assistant emailed me and thinks I have wrong batt ID set up so I will be checking thatTexican, I too was looking for EG4 battery bank to work with LV6548. I spoke to watts247 who said EG4 not communicate with LV6548, and was recommended Pytes 5.1KW batteries; pretty slick how batteries connect in parallel with snapon cable clips. I also saw Will Prowse using SOK 5.1KW batteries with LV6548. I'm trying to decide which ones to get (Pytes or SOK), but really like EG4.
You should start your own thread. To avoid confusion.I have a question on a somewhat related issue, not sure if anyone can offer any guidance.
I’m trying to understand the wiring diagram and circuit breaker requirements from the main breaker to 5 LV6548 inverters AC input, then the 5 inverters AC output to sub panel?
Inverters 1-3 are in 1st phase, inverters 4-5 are in 2nd phase.
Plan is to program LV6548’s to provide power by priority: 1) solar (19.6kW); 2) batteries (41kW); 3) grid.
What I have gathered from other threads, for split phase with two units I would install a 60a 2-pole circuit breaker on main panel and run one hot to 1st phase inverter and one hot to 2nd phase inverter. Then I would run AC output for both inverters to the sub panel to another 60a 2-pole circuit breaker.
Not sure how to configure this for 5 inverters?
Also, intermittently to reduce idle energy consumption and when high demand is not necessary, the plan is to turn off inverters 2-3 of 1st phase and inverter 5 of 2nd phase to run system with 2 units in split phase.
I have not purchased the sub panel yet, the main panel is a Square D Homeline, so any input on sub panel models with 40 spaces or more in the same line would be appreciated so I can recycle all the current circuit breakers by transferring them to the sub panel.
I’ve also considered a “smart” sub panel (i.e. Lumin) for load management. Experience in this area is appreciated as well.
Thanks for any guidance.