Background: I’ve got a potential project to inspect multiple off-grid homes and their solar systems. For purposes of scope I’m simply interested in evaluating if these home owners have over spent on large generators where they’re unable to utilize the full output potential of their generator investment.
Things to keep in mind I’m not considering brands of generators, their reliability, outdoor rating, fuel type or anything else other than their continuous output and purchase price.
Scenario:
The home has a generator capable of a continuous output of 22kW at 240v. The generator is attached to the gen input on a Sol-Ark 12k. According to the spec sheet for the Sol-Ark 12k the maximum amperage in/out DC is 185 amps.
Spec sheet: https://www.sol-ark.com/wp-content/uploads/12K-2P_SpecSheet.pdf
If the generator was producing 22kW, and if the inverter was able to convert 100% of this energy to dc at 51.2v, my rough math shows 429 amps dc. So if the Sol-Ark 12k can only output 185 to the batteries then there is an excess of approximately 244 dc amps of capacity unutilized from the generator.
In this scenario I could potentially conclude that the generator is over double the size needed if the goal was to match the generator closer to an inverter that could make use of the generators entire rated continuous output.
I realize that the generator might also have some utilization for loads while charging, but for purposes of charging only I’m omitting this consideration.
In the scenario above if the conclusion is accurate (ish) what would be the ideal generator size for the stated configuration. I’m looking for any figures that include a potential for a little bit of extra capacity based on any sorta rules of thumb.
Thank you in advance for any suggestions/corrections/guidance. ?
Background: I’ve got a potential project to inspect multiple off-grid homes and their solar systems. For purposes of scope I’m simply interested in evaluating if these home owners have over spent on large generators where they’re unable to utilize the full output potential of their generator investment.
Things to keep in mind I’m not considering brands of generators, their reliability, outdoor rating, fuel type or anything else other than their continuous output and purchase price.
Scenario:
The home has a generator capable of a continuous output of 22kW at 240v. The generator is attached to the gen input on a Sol-Ark 12k. According to the spec sheet for the Sol-Ark 12k the maximum amperage in/out DC is 185 amps.
Spec sheet: https://www.sol-ark.com/wp-content/uploads/12K-2P_SpecSheet.pdf
If the generator was producing 22kW, and if the inverter was able to convert 100% of this energy to dc at 51.2v, my rough math shows 429 amps dc. So if the Sol-Ark 12k can only output 185 to the batteries then there is an excess of approximately 244 dc amps of capacity unutilized from the generator.
In this scenario I could potentially conclude that the generator is over double the size needed if the goal was to match the generator closer to an inverter that could make use of the generators entire rated continuous output.
I realize that the generator might also have some utilization for loads while charging, but for purposes of charging only I’m omitting this consideration.
In the scenario above if the conclusion is accurate (ish) what would be the ideal generator size for the stated configuration. I’m looking for any figures that include a potential for a little bit of extra capacity based on any sorta rules of thumb.
Thank you in advance for any suggestions/corrections/guidance. ?