Howdy all - wondering if any Sol-Ark guys have ever seen this. Sol-Ark is commanding the generator on, but not accepting any charge to batteries, and actually shows power going in reverse direction as usual, towards generator. I attached a picture. What the heck is going on here lol
 

Attachments

  • IMG_3789.jpeg
    IMG_3789.jpeg
    220.8 KB · Views: 28
It shouldn't be doing that if the port is set as a generator input.
I would double check the settings. As it is configurable as both an input or an output.
 
What settings you think I should check?
Assuming generator is on the Gen Input:
Batt Setup Screen
Smart Load Tab
None of the boxes should be checked.

Assuming Generator is on the Grid Input:
Depending upon your firmware version
Old Firmware:
Grid Param screen
Sell Control Tab
Gen Connected to Grid Input - check the box.
Zero Export Power 10w or higher

New firmware (2023 version of the manual)
Limiter Screen
Other Tab
Gen Connected to Grid Input - check the box.
Zero Export Power 10w or higher

If you are off-grid, you may also want to:
Limiter Tab
Grid Sell - Uncheck
Limit Power to Load - Checked

Also worth checking (for the sake of the generator):
Basic Setup Screen
Advanced Tab
Gen Limit Power
Set to 80% of your generator's run capacity.
 
Assuming generator is on the Gen Input:
Batt Setup Screen
Smart Load Tab
None of the boxes should be checked.

Assuming Generator is on the Grid Input:
Depending upon your firmware version
Old Firmware:
Grid Param screen
Sell Control Tab
Gen Connected to Grid Input - check the box.
Zero Export Power 10w or higher

New firmware (2023 version of the manual)
Limiter Screen
Other Tab
Gen Connected to Grid Input - check the box.
Zero Export Power 10w or higher

If you are off-grid, you may also want to:
Limiter Tab
Grid Sell - Uncheck
Limit Power to Load - Checked

Also worth checking (for the sake of the generator):
Basic Setup Screen
Advanced Tab
Gen Limit Power
Set to 80% of your generator's run capacity.
Ok thanks DIYrich, I’ll check that. I know I do have generator on grid, and I checked the ‘gen to grid input’, but the rest I’ll check on tonight, I’m in the new firmware. Could any of those explain it working when on % mode, then doing this on V mode?
 
Don't forget to update the thread with your findings, is that a 12k or a 15k?
 