The inverter on one of my clients is giving error 08 after being connected to the grid for a while. I suspect 2 main problems:
- there's some kind of neutral bound on the inverter input such as a generator with a common neutral from somewhere close. (not likely)
- the charging current and voltage are a bit on the edge and thus going into "bus voltage high" after the charging voltage has reached the BMS max voltage causing the chgmos to stop accepting current. resulting in a spike caused by sudden cut of current flow, causing an overshoot in charging voltage, thus the error 08 problem.
will follow up with the results.
- there's some kind of neutral bound on the inverter input such as a generator with a common neutral from somewhere close. (not likely)
- the charging current and voltage are a bit on the edge and thus going into "bus voltage high" after the charging voltage has reached the BMS max voltage causing the chgmos to stop accepting current. resulting in a spike caused by sudden cut of current flow, causing an overshoot in charging voltage, thus the error 08 problem.