Growatt SPF 5000 ES - 5108 Bus voltage high(Fault)

The inverter on one of my clients is giving error 08 after being connected to the grid for a while. I suspect 2 main problems:

- there's some kind of neutral bound on the inverter input such as a generator with a common neutral from somewhere close. (not likely)
- the charging current and voltage are a bit on the edge and thus going into "bus voltage high" after the charging voltage has reached the BMS max voltage causing the chgmos to stop accepting current. resulting in a spike caused by sudden cut of current flow, causing an overshoot in charging voltage, thus the error 08 problem.

will follow up with the results.
 
Any luck in finding the solution to this 08 error? I am still facing it when battery charge reaches 100%.
(I managed to keep the frequency of it happening lower by reducing charge current to less than 40A)

If i set charge current to 50A the error is sure to come within a few minutes. (I have tested it with 3 inverters already and same issue)

Setup is 6 Panels+Inverter+Battery
 