This can all be overwhelming at first - but stick with it and it will make a lot of sense over time.
Did your inspector give you a written report with all the issues flagged? If not did you take lots of really good notes? You may also be able to get a copy of this report if you didn't get one at the time.
They typically will NOT tell you how to do things and that can put them on the hook for the design flaws. But they will tell you which sections of the NEC you violate. You can get free access to the NEC from a sticky in the main forum.
Energy audit? what are you trying to power?
Are you going grid tied or off grid?
Are you doing battery bank or just when the sun shines?
Are you going to back-feed the grid or be net-zero?
Equipment list? For inspections typically everything needs to be UL listed down to the crimps on your wires.
From the pictures and all my studying on this forum you would have to start by taking apart all your wiring and boxes and connections and start over before you could be code compliant.
First - you need a well drawn plan that is what the call a single line design. Basically instead of showing the individual conductors you show the groups and where they connect to and from. There are a variety of programs, but draw.io is free and many people use it. You may end up with a bunch of drawings for different aspects of your install, but if you do grid tie they will usually require that.
Second - if you need to pass inspection you need to know the rules. So, find out what version of the NEC your county uses and also the state and get the correct version of this book - I suspect you will find it is the NEC2020 version but check first. Then you can lookup stuff and see what the book says and also come here are ask questions.
Electrical jobs
www.mikeholt.com
Electrical jobs
www.mikeholt.com
For free check this resource out and see what applies to you - pay particular attention to page 15
https://newbuildings.org/wp-content/uploads/2022/11/2020-NEC-Solar-and-Storage-Single-Family-Perm-and-Insp-Guide.pdf
diysolarforum.com
And poke through the resources section at the top for examples of drawings and everything else you might need.
Generally trades people will not even bid on or look at a job like this because it will take them a day to figure out what is there are where to start. Not worth their time to figure it all out and bid then be turned down because the price is high. Not saying this is your case. So if you want someone to do the work for you, you will have to provide them with clean plans of what you have so they can just look at it.
One tip - ground rods can only have 6" exposed and they can not be cut off if they get hard to drive. Another tip is where ever your inverter is there should be a ground wire attached. If the inverter is the only source of power then it will have a ground rod or a pair of rods 8ft apart, but connected by a single unbroken wire to the inverter so rod-rod-inverter, everything else is attached to this single ground to prevent shock hazards. This wire is generally #6 but check the code book for your area.
If it is grid tied it will have a ground to the main panel. In any case the wires to your panels should also include an extra ground wire that attaches to anything metal out there. There should NOT be a ground rod at each panel mount or you will have ground loops and it will cause you major issue.
Typically RSD are not required unless you are doing roof mount. That is unless the county or state you are in requires them for every install.
Another thing is if you leave the wiring and everything above ground at the panel mount site it usually requires a fence around it to keep people from the potentially dangerous voltages. I am not telling you to build I fence, I am telling you to check your local code or the NEC whichever is more strict.
An last but not least, don't be afraid to ask questions - especially if you don't understand an answer or WHY something is done the way it is.
Wow! Thank you so much for your response, time and patience! Let me digest this all.
I will try to cover everything.
1yr ago this project is to ONLY power my detached shop (70' from house), where my home office, freezers, fridges, etc, are, in case of lengthy power outages. We do have power out a few times a year, 2 in the last week. This project was to keep me out of trouble, and I wanted to learn, so when it has issues.... Yea, Im
that guy
Energy audit?
-No
What are you trying to power?
-Shop only
Are you going grid tied or off grid?
-For now, just shop, then maybe power the house, but not selling it, no net metering.
Are you doing battery bank or just when the sun shines?
-Yes
Are you going to back-feed the grid or be net-zero?
-No, just want self-sufficiency.
Equipment list?
-Yep, got that, details below.
For inspections typically everything needs to be UL listed down to the crimps on your wires.
-Well that's going to be fun!
Inspector
I had the inspector out back in Sept, to approve covering the Sch40 buried between the cutoff switch at the array, and the side of the shop. He approved that. The rest he would need way more time to review, and he wants to do all of it end to end (Solar panel to electrical panel).
Inverters
I now have (at rear of shop) 2 EG4 18kpv in parallel (mounted on 1/2" ply topped with Hardie Backer). AC Power output via flex metal conduit going to 4x4 boxes to a Siemens 125 amp panel with 2 50amp breakers. That feeds into a 3-3-3-5 copper Ser cable into the attic floor (Tacked to 2x4s buffered by lateral 2x4s to block insulation), down into the 125 amp C-Hammer sub panel (at front of shop) to a 100amp breaker with an interlock to the 60 amp from the house.
Batteries
There are 9 48v LFP (15cell) battery bank and a dual 48v FLA extreme deep cycle battery banks (8*6v). (hence the DC switch)
Gen
A grounded, and Zombie Boxed 9500 Predator Generator (W Neutral clipped from gnd) connected via the L14-30 (4 wire, W/ appropriate sticker) connected to the Gen Inputs. Inverter controls load to 5.5kw total.
Grounds
For the inverters there is a ground rod just on the other side of the wall (Back of the shop) as well as connected to the Shop Sub panel ground via the Ser cable.
Ground for the Array, I was just told yesterday, needed to be #4 bare copper.... So, redo.....and yes agreed, those rods are way too high.
BUT, if I only need to have 2 (8' apart) and I put those over by the tracker that has the combiner and blade cut off switch. If #4 wire is true, then I will redo all that.
RSD
It was just part of the package, but eventually there will be panels put on top of the roof of the shop, and on the South Facing wall, I just need to get what I have so far signed off on.
Plans
As for plans, I have multiple Visio diagrams of 1 and 3 wire plans for Overall, the solar side, and Post Inverters AC side. I also have the 3 wire plans from EG4 for my use case (off grid plan fits best for my scenario).
Quandaries
Conduit watertight?
I was also told that the Conduit that goes between the trackers would need to be watertight coupled, meaning I would have to pull ALL the wires and redo all of them. Well, while I'm redoing all the ground rods and wires......
Conduit DC power cables???
An electrician told me the 2/0 marine (Gregs Marine) tinned wires going between banks, battery bank switch, busbars and inverters are hanging loose and need to be in boxes (for the busbars and switch) and conduit (The liquid tight flexible gray kind) That I am stumped on, as its NOT that flexible! And I have contacted Inverter supply, and other stores on a solution, but there are none, and no one is calling for DC Breaker boxes with Busbars. There are a couple out there, but they are made for specific inverters.
I also know that the main 200 amp panel in the house would need to be replaced with a 400amp, and an auto transfer switch put in, but those are another chunk I am not ready for at this point.
I have tons of Pics for all of this, let me know.