Nice drawing! I wish I had the ability to do that.
Should stick to the breaker size listing in the manual for sizing AC in and AC out. You can use a 100a sub panel* even if you feed it with a 40a breaker so long as you keep in mind that it is a 40 amp max service. Your line 5 would have a breaker where it comes off the Main and should be drawn in the Main Panel. That way there is no question of back feed. You might also want to label AC In (5) and AC Out (2) so there is no question of current flow.
* panel ratings are based on max service and they can always be used for less. Just like you can have branch circuit breakers in the panel that add up to more than what ever the panel is fed with. Breakers are sized to protect load and wires feeding loads.
Should stick to the breaker size listing in the manual for sizing AC in and AC out. You can use a 100a sub panel* even if you feed it with a 40a breaker so long as you keep in mind that it is a 40 amp max service. Your line 5 would have a breaker where it comes off the Main and should be drawn in the Main Panel. That way there is no question of back feed. You might also want to label AC In (5) and AC Out (2) so there is no question of current flow.