JK BMS reading negative amps with no load and PV's on

tjstepanian

New Member
Joined
Jan 4, 2023
Messages
39
Location
Central Cal
So I have a LV6548, using a JK BMS B2A20S20P with LIFepo4 16s config battery. After going through botched updates last week on my BMS (IOS phone), I now noticed under NO load with the PV's on (3S2P 250 watt) panels...when viewing my bms app, I see -16 amps while voltage climbs to full SOC. My Ah reading begins to drop as well

If I shut off breakers to PV's... Amps go to +1.2 Amps. Or at night when there is no sun the BMS will read positive Amps as well

Not sure if this is another botched reading from the BMS or do I have an issue with my PV connections ? I made sure I have correct polarities from the panels to the SCC. I believe SCC is configured correctly.

Anybody experience this ??
 
Need to calibrate the current to zero in the BMS settings
 
Hello, I believe I am having the same issue. Is there a particular page in the manual with the instructions to calibrate the current to zero in the BMS settings?
 