Here is my current Setup
200Amp Main Panel
100Amp Detached Garage Panel With it’s own Grounding Rods
50 amp (6 awg wire) RV outlet from Garage panel, but it is mounted on the house.
Solar Circuits Panel in Detached Garage Also Bond / Neutral Separate
EG4 3000
I want to now do, Is Take over some circuits in the house (Fridge and some lighting)
My plan is to eliminate the 50amp RV plug and Run conduit to an additional “critical loads” panel near the main panel. Pull the loads out of the main panel completely, and Add to my CL panel I will move the 6awg wire to the solar circuits panel and Just land it to a 30amp breaker.
I realize I will only be able to utilize one hot leg of the RV connection (120v) until I purchase a 2nd Eg4 3000 and move to split phase
What are the Flaws / Concerns in my plan? Please Critique. pic with basic layout