Hello, does anyone know where to find more info on how this thing actually operates? The manual that came with it seems to be lacking a lot of detail. My situation...
I have 24 240w panels wired in 2 banks of 12. 3 panels are wired together to get a max of 111v then go to 2 combiner boxes. From that 4awg goes to the inverter 1 60' run and the other 80'. 16 Trojan RE-16B batteries in 2 banks then paralleled together 3/0 wire to the inverter with a 300amp breaker. No generator or utility service connected yet, The line out is just chopped off gang outlet currently.
Everything seems to charge up fine and operate correctly when the unit is off mode, seems to do fine in inverter mode too other than the first array only shows voltage coming in and no watts. Switched it off, checked fuses, reset, and then wattage appeared for a bit then when back to zero in inverter mode.
If flooded batteries are selected it shows a voltage cutoff of 42v. seems like the batteries would be almost dead instead of at 50% to preserve their life.
Based on the specs it shows the thing will only accept 120v for an input but not 240? Also the wiring size to a panel is recommended at 10awg? Seems pretty undersized going to a panel. Also today plugged in an angle grinder....7.5 amp max and the thing shot a fault 72 code and I have no idea what that means.
Anyways, long story short I just don't know what the thing is doing and why...would like to find out more but don't know where to look.
I have 24 240w panels wired in 2 banks of 12. 3 panels are wired together to get a max of 111v then go to 2 combiner boxes. From that 4awg goes to the inverter 1 60' run and the other 80'. 16 Trojan RE-16B batteries in 2 banks then paralleled together 3/0 wire to the inverter with a 300amp breaker. No generator or utility service connected yet, The line out is just chopped off gang outlet currently.
Everything seems to charge up fine and operate correctly when the unit is off mode, seems to do fine in inverter mode too other than the first array only shows voltage coming in and no watts. Switched it off, checked fuses, reset, and then wattage appeared for a bit then when back to zero in inverter mode.
If flooded batteries are selected it shows a voltage cutoff of 42v. seems like the batteries would be almost dead instead of at 50% to preserve their life.
Based on the specs it shows the thing will only accept 120v for an input but not 240? Also the wiring size to a panel is recommended at 10awg? Seems pretty undersized going to a panel. Also today plugged in an angle grinder....7.5 amp max and the thing shot a fault 72 code and I have no idea what that means.
Anyways, long story short I just don't know what the thing is doing and why...would like to find out more but don't know where to look.