LV6048 MPPT + 4 x 200W Solar Panels: Best Panel Wiring Config

SIGEPJEDI

New Member
Joined
May 31, 2023
Messages
2
Location
Columbus, OH
Curious recommendations on wiring configuration as having all 4 panels in series is over the LV6048's max solar voltage.

A mixed configuration, 2 in Series + 2 in Series, then all wired together in Parallel - This is just over the Max Voltage

I could use the second PV controller on the LV6048 and have two sets of 2 panels in series.... This just seems like a lot of wires for basic? functionality of 4 panels.

Specs of both LV6048 MPPT and Solar panels are attached below.

Thanks in advance for recommendations and best approach.

Screen Shot 2023-06-05 at 4.34.06 PM.pngScreen Shot 2023-06-05 at 4.34.30 PM.png
 
Curious recommendations on wiring configuration as having all 4 panels in series is over the LV6048's max solar voltage.

A mixed configuration, 2 in Series + 2 in Series, then all wired together in Parallel - This is just over the Max Voltage

I could use the second PV controller on the LV6048 and have two sets of 2 panels in series.... This just seems like a lot of wires for basic? functionality of 4 panels.

Specs of both LV6048 MPPT and Solar panels are attached below.

Thanks in advance for recommendations and best approach.

View attachment 151801View attachment 151802
You should be able to put 3 in series and then parallel. I have same unit and have 12 panel 4 arays of 3 in series and then parallel.
 

Attachments

  • 20231020_142425.jpg
    20231020_142425.jpg
    2.4 MB · Views: 5
Curious recommendations on wiring configuration as having all 4 panels in series is over the LV6048's max solar voltage.

A mixed configuration, 2 in Series + 2 in Series, then all wired together in Parallel - This is just over the Max Voltage

I could use the second PV controller on the LV6048 and have two sets of 2 panels in series.... This just seems like a lot of wires for basic? functionality of 4 panels.

Specs of both LV6048 MPPT and Solar panels are attached below.

Thanks in advance for recommendations and best approach.

View attachment 151801View attachment 151802
I would get a combiner box and connect all panels to box and then 2 cables neg and pos to the controller from that box
 

Attachments

  • 20231019_184947.jpg
    20231019_184947.jpg
    870.5 KB · Views: 3
You should be able to put 3 in series and then parallel. I have same unit and have 12 panel 4 arays of 3 in series and then parallel.
Thats how i have it. But shuts down solar once batts are full.
 

Attachments

  • 20231115_143201.jpg
    20231115_143201.jpg
    600.6 KB · Views: 3