CerDaw
New Member
Hi,
We have installed a microhydro system, using a powerspout PLT80 turbine, 70 m head, 140 m pipe run, Flow rate 3L per second. Pipe diameter is 55 mm. Cable is 25mm^2 2-core at 130 m long. Long length but oversized cable to reduce power loss. High head, low flow site.
DIY setup, specs from calculations
OuputVoltage: 84 V
CableEfficiency: 95 %
CableLength: 135 m
LoadVoltage: 80 V
ActualLoadVoltage: 80 V
CableMaterial: Aluminium
CableSize: 16.773 mm^2
CableAWG: 5 AWG
CableCurrent: 7.6 A
ActualCableEfficiency: 95 %
ActualTotalOutput: 611 W
Pipe is full of water, at maximum capacity , could not get more water in it if we tried so running at full capacity. Turbine Pressure guage (located 5 cm from turbine input) is at 50 psi . Twin valves in turbine at 6 mm opening each. Alignment appears fine and bearings greased but first thing we noticed is the PLT wheel wont spin by itself, we have to manually give it a push, and then water flow will keep it going. If we disconnect water , it slows and stops pretty fast, like it is running under resistance and does not keep spinning under its own momentum. The turbine came to us fully assembled so we have not assembled it. Will take a video in next day and post. We're reading around 50 V at the turbine with a multimetre.
At power shed, we're running a midnite classic 250, idle voltage (drawn from battery bank) is 37 V. When turbine is operational, voltage goes to 45 V and wont go over it, it does seem to fluctuate between 40-45 V every few minutes. Classic controller shows no generation, which isn't unexpected since the voltage being read is low.
What are we missing and why is the voltage reaching our power shed so low considering the drop isn't much (though it is higher than expected). Should we be getting higher than 50 PSI at the turbine with those specs? Would you expect it to be higher? Any help and suggestions please. Should the turbine spin freer or have some resistence?
Will get photos up in next few days. Thanks
We have installed a microhydro system, using a powerspout PLT80 turbine, 70 m head, 140 m pipe run, Flow rate 3L per second. Pipe diameter is 55 mm. Cable is 25mm^2 2-core at 130 m long. Long length but oversized cable to reduce power loss. High head, low flow site.
DIY setup, specs from calculations
OuputVoltage: 84 V
CableEfficiency: 95 %
CableLength: 135 m
LoadVoltage: 80 V
ActualLoadVoltage: 80 V
CableMaterial: Aluminium
CableSize: 16.773 mm^2
CableAWG: 5 AWG
CableCurrent: 7.6 A
ActualCableEfficiency: 95 %
ActualTotalOutput: 611 W
Pipe is full of water, at maximum capacity , could not get more water in it if we tried so running at full capacity. Turbine Pressure guage (located 5 cm from turbine input) is at 50 psi . Twin valves in turbine at 6 mm opening each. Alignment appears fine and bearings greased but first thing we noticed is the PLT wheel wont spin by itself, we have to manually give it a push, and then water flow will keep it going. If we disconnect water , it slows and stops pretty fast, like it is running under resistance and does not keep spinning under its own momentum. The turbine came to us fully assembled so we have not assembled it. Will take a video in next day and post. We're reading around 50 V at the turbine with a multimetre.
At power shed, we're running a midnite classic 250, idle voltage (drawn from battery bank) is 37 V. When turbine is operational, voltage goes to 45 V and wont go over it, it does seem to fluctuate between 40-45 V every few minutes. Classic controller shows no generation, which isn't unexpected since the voltage being read is low.
What are we missing and why is the voltage reaching our power shed so low considering the drop isn't much (though it is higher than expected). Should we be getting higher than 50 PSI at the turbine with those specs? Would you expect it to be higher? Any help and suggestions please. Should the turbine spin freer or have some resistence?
Will get photos up in next few days. Thanks