Grid interactive (hybrid inverter) has an AC input 'pass-through' relay. Some have two AC inputs with two pass-through relays for grid input or generator input. Only one input is used at a time with grid input usually taking priority if it is available,
Inverter is always connected to AC output. Inverter can be active, in which case the AC input pass-though relay must be initially open when AC input is first applied.
In standby mode the inverter remains inactive but the control circuitry pre-syncs to the AC input before closing pass-through relay from AC input.
AC input terminals are initially measured for AC voltage and phasing. With pass-through relay initially open the inverter freq/phasing and AC voltage is slowly adjusted to match phase and voltage of AC input. This can take a couple of seconds, up to 10 seconds, depending on frequency span limits set for inverter.
During sync'g process, the inverter will only slew its phasing at no more than about 0.3 Hz per second rate. This is to avoid disturbing possible loads like AC motors that would create forward or reverse surge currents if AC phase is abruptly shifted.
Due to the limited phase adjustment rate, the wider the inverter allowed AC input frequency locking range, the longer the possible phase lock time and the longer the possible time before pass-through relay closes.
Once inverter syncs to AC input the pass-through relay is closed putting inverter and AC output in parallel with AC input.
UPS mode and battery charging runs inverter active in parallel with AC input. If AC input is connected to grid and grid drops outs, there will be a momentary overload of inverter which it detects and opens pass-through relay releasing from AC input. There is a short voltage glitch on AC output due to momentary inverter overload before pass-through relay is released but most appliances ride through the short glitch of up to 8 milliseconds, or about a half AC input cycle maximum length of time.
Because the inverter is connected in parallel with grid it needs to meet minimum requirements to recognize and release from grid in a short amount of time to prevent back feeding grid under grid failure conditions.