Hi All,
It's been a while since I posted here. I'm building an off-gird system using Sunny Island battery inverters/chargers. The Sunny Island AC1 terminal connects to a stand-alone breaker panel via a 70A single-pole breaker. This breaker is obviously back-fed by the Sunny Island. NEC 2017, rule 408.36(D), states
I have been searching for breaker panels that have a hold down kit for a single-pole breaker, and options appear limited. I was told Square D QO panels do not have such a kit. Siemens PN panels don't appear to either. What are you folks using? I wouldn't want to fail an inspection on such a trivial issue.
Thanks!
It's been a while since I posted here. I'm building an off-gird system using Sunny Island battery inverters/chargers. The Sunny Island AC1 terminal connects to a stand-alone breaker panel via a 70A single-pole breaker. This breaker is obviously back-fed by the Sunny Island. NEC 2017, rule 408.36(D), states
Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.
I have been searching for breaker panels that have a hold down kit for a single-pole breaker, and options appear limited. I was told Square D QO panels do not have such a kit. Siemens PN panels don't appear to either. What are you folks using? I wouldn't want to fail an inspection on such a trivial issue.