zanydroid
Solar Wizard
What is the AWG on this branch circuit/feeders to the service? The voltage drop on grid tie inverter output circuits shows up as a rise at the inverter
12 AWG from Inverter to Meter/panel. 4/0 to Utility transformerWhat is the AWG on this branch circuit/feeders to the service? The voltage drop on grid tie inverter output circuits shows up as a rise at the inverter
Yeah, I heard a lot of bad things about solar edge but i figured i’d give it a shot.Mine also have a settable wattage limit. One I picked up was set at around 80% of nameplate power.
Not sure, but Ethernet comms might be used in mine to dynamically change that value, to implement zero or limited export.
Apparently updated to NVM on occasion.
Whatever you're experiencing right now is probably operator error. I'm sure the company's products normally come up delivering the proper amount of power. It is just their reliability record that concerns me.
I've been happy with SMA. But they've recently discontinued some products, new model isn't available yet, and looks like price will be up significantly, especially to the street price previous model had been going for.
Here in California, only battery systems will make sense for new installs. You're probably aware of such rule changes are on the horizon in NJ.
Good To Know. Always curious about that.Probably will draw very little power with no optimizers installed. There's no MPPT in a SolarEdge inverter so it doesn't know how to deal with the power curve on a bare solar panel.
So first I check for Ohms on the input and output sides on the optimizer. according to Solar edge, if under 100ohms, replace. All tested above.You said you tested the optimizers before installation. What was that procedure?
What is the string voltage when the sun is up but inverter off? Should be 1 volt per optimizer.
Can you double check you've got the string wired up correctly? It would be hard to have some panels/optimizers hooked up reverse polarity, but I think it's worth double checking.
It's probably also work triple checking for bad connections through the entire string.
At this point, I think your right, it's operator error, but considering your experience it may be you have a faulty inverter. If, after double checking everything, you still don't find anything, I'd ask Solar Edge for some warranty replacement parts.
Ok, I thought maybe you had some way to function test the optimizers. Checking for shorts is a good idea.So first I check for Ohms on the input and output sides on the optimizer. according to Solar edge, if under 100ohms, replace. All tested above.
That's odd, I don't know what higher voltage means, if anything.Next I connected the panel to the optimizer. While the sun was hitting panel, I tested output voltage. All fell with range. all read 1.01Vdc.
Next I hooked them all together and tested total output, which came to 14.1Vdc.
Only thing I will say is that at inverter I'm getting 15.4Vdc. Solar edge told me that could be due to wire size from inverter to first opt. I used 10AWG from inverter to Opt about 25 ft.
Given all your testing, I'd request a warranty replacement from Solar Edge. It doesn't make sense what's going on.I ended up remaking connections with new MC4 and was still reading 15.4. All optimizers are reporting correctly and all proper voltages/ Amps for S440.
Thats something that is bothering me. Cause everyone says however many panels is the voltage.. but solar edge is telling me ok.Ok, I thought maybe you had some way to function test the optimizers. Checking for shorts is a good idea.
That's odd, I don't know what higher voltage means, if anything.
Mine doesn't do that. When I had 20 panels/optimizers it was pretty close to 20 volts. Now with 24 panels/optimizers it shows roughly 24 volts.
I was sort of hoping you'd say 12 volts from your 14 optimizers, or something similar.
Given all your testing, I'd request a warranty replacement from Solar Edge. It doesn't make sense what's going on.
When you did the factor reset. Did you try just connecting the panels, pairing the optimizers and turning it on? Not messing with any settings?
So when the tech told me string was over sized by 80 Watts. I removed 1 panel. my Voltage on string topside was 13.1 but readying 14.4 at inverter.Wire gauge isn't going to affect voltage at zero amps.
Capacitor in inverter could change voltage read from DC/DC circuit that has ripple, if that is how they deliver 1V.
Can you reduce number in series until the wattage output decreases? (Binary search reduces number of steps.)
Determine if that matches expected watts from that number of panels, or if you dropped below minimum voltage.
Thus far, removing a panel has maintained same output, correct? Starting to look like optimizers are working, but inverter is capping output.
Removing many would confirm this.
So first I check for Ohms on the input and output sides on the optimizer. according to Solar edge, if under 100ohms, replace. All tested above.
Do you have something recording and plotting voltage at the panel side of the inverter circuit, as you change stuff? Besides the voltage monitoring reported by the SE.First Im gonna disconnect the existing solar so that there is no other backfeed. Also gonna run my double oven electric stove. (pulls about 9000 Watts.)
Yeah. Panels were tested iI interpreted your previous message as saying you also tested the panels before putting them into the optimizer.
I have a sense monitor that feeds me info like high and low voltages.Do you have something recording and plotting voltage at the panel side of the inverter circuit, as you change stuff? Besides the voltage monitoring reported by the SE.
yeah, All New products. Will they give me warranty replacement when they are telling me nothing is wrong on their end?Sounds frustrating, I've never heard of anyone having an issue like this with Solar Edge. There aren't many Solar Edge installs here, so that's not a great data point.
Did you buy this all new? If so, request some warranty replacements from SE. If not, maybe there's a reason they were being sold...
Yeah That’s what i was showing too.I just punched your array into PVwatts. It should hit 3500 ish at something like 10 am, then drops down for the afternoon.
Can you post your daily graphs?
yeah, All New products. Will they give me warranty replacement when they are telling me nothing is wrong on their end?
The fault means exactly what it says. One line to neutral measured high voltage. I'd check the neutral connection.Oh also I had one error code which im not sure what it means. Never seen it before. it showed up on 2/15 just once.
Grid line to Neutral over Voltage Fault
If you want to ship the inverter to California (and back) I can hook it up to a (12 x 325) 3900 watt string or two, for a test.
I'm surprised Solar Edge isn't any help. But, they may need to see more sunny days to gather good data.