so technically the over voltage shut-off is a secondary guard while frequency shifting being the primary throttling ? would that be sufficient to avoid a dump-load requirement to prevent smoke (other than throwing away production) ? typically solar inverters are designed to keep cycling to check grid-AC integrity anyway, such as during outages, which can go for hours/days.The only thing that will happen if you don't consume or discard the excess energy is that the AC voltage will rise to unacceptable levels on the inverter outputs and your house, and once that happens the AC-coupled PV inverters will turn off completely. They are required by law to disconnect from the AC source immediately when the voltage level becomes abnormal. They will then wait for around 5 minutes before they will start sampling the voltage levels again and then turn on if all is right.
Also, is generator AC clean enough to AC-couple ? may be the newer inverter type generator. Has anyone successfully AC-coupled from generator power ? Thank you, it's like the more I learn the more I don't know