diy solar

diy solar

Not connected to grid, solar through house circuit possible?

iampob

New Member
Joined
Apr 18, 2024
Messages
48
Location
Santa Fe, New Mexico
HI,

trying to figure out what our best options are on a budget,
I got 16 370W NEC panels, and I'm slowly learning what the regulations are and permits required.
Our energy usage is pretty low, a 5kW system should cover it.

One of the things (of many!) I'm not understanding yet, is it possible to not be connected to PNMs grid but still have the solar providing energy to the house circuits, and when no solar is being produced it’ll use the grid?

I’m not against being connected to the grid, just wondering if it is possible without, as PNM now have additional compliance required, which may limit options for inverters/equipment.

effective March 29, 2024, all applications for interconnection must specify advanced inverters compliant with IEEE 1547-2018.

At the moment I don’t think we can include a battery, or at least not a large one,
loose calculations are about 2k for Unirac RM10, we have a TPO roof, which is pretty new and would like to use ballast mounts if possible. Then if we go with micro inverters about 2k for those.

thanks
 
loose calculations are about 2k for Unirac RM10, we have a TPO roof, which is pretty new and would like to use ballast mounts if possible. Then if we go with micro inverters about 2k for those.

thanks
Microinverters are not a great idea for a simple off grid system. If you want to go simple, get an AIO inverter (there are dozens to choose from) a battery and then arrange the solar to not overvolt the AIO's solar inputs.
 
EP Cube w/at least 9.9KWH battery, add battery as needed, simple, quick, & legal everywhere.
NOTE: Signature Solar has on sale a few more days for $9,051 (free ship) less Fed tax credit = $6,472. & no need for microinverters or anything else.
 
Last edited:
Thanks for the info, PNM Interconnection is $150-300 max I think,
would love to get the EP Cube, looks very simple, unfortunately about 6K over our budget, and doesn't look like it has the IEEE 1547-2018 certification PNM are requiring.

So if we can't yet afford to go with a battery, is the only way to get solar coming through the house plugs to get the interconnection set up with PNM? or is it possible to not be connected to PNM, but have the system switch between solar when it's available and PNM when it's not?
I guess I'm a little confused about what "Off grid" can be, is it strictly that you don't have a power company account and no energy connection to them?, or can it be that that you do have their grid power coming in, but your solar system can work totally independently from them?
hope that makes sense.
 
So if we can't yet afford to go with a battery, is the only way to get solar coming through the house plugs to get the interconnection set up with PNM?
Yes, and you have to get a grid tie agreement as well, which means getting plans signed off, an inspection etc.
 
So if we can't yet afford to go with a battery, is the only way to get solar coming through the house plugs to get the interconnection set up with PNM? or is it possible to not be connected to PNM, but have the system switch between solar when it's available and PNM when it's not?
You might not need an interconnection agreement if the inverter cannot export to the grid, such as the 6000xp.
 
Thanks, I'll check out what's possible with it.
This thread has some useful info I think, maybe I could have a separate panel with just some circuits running of the solar?
 
Last edited:
Looks like there are only a few states so far where IEEE 1547-2018 is required,
I haven't found a decently priced compliant inverter yet, the IQ8 micro inverters are compliant.

 

Attachments

  • Screenshot 2024-05-13 at 10.05.41 AM.png
    Screenshot 2024-05-13 at 10.05.41 AM.png
    249.1 KB · Views: 7
Looks like there are only a few states so far where IEEE 1547-2018 is required,
I haven't found a decently priced compliant inverter yet, the IQ8 micro inverters are compliant.

That is for exporting inverters. If he uses an off grid inverter, it is normal load to the grid.
 
Thanks,
so this requirement is only if we wanted to use PNM net metering? we could still have an interconnection to PNM without IEEE 1547-2018?

this is from PNMs page

Pursuant to 17.9.568.11 NMAC and the New Mexico Public Regulation Commission's Order Regarding Joint Status Report issued in the 23-00203-UT docket on December 14, 2023, is effective March 29, 2024, all applications for interconnection must specify advanced inverters compliant with IEEE 1547-2018 including proposed updates to existing systems.
 
Hi,

just stumbled across this video, one of the examples he gives is with dynamic bonding (at 2:50), it looks like it could work so we could have solar coming into the house circuits and be separate from the grid, so we wouldn't have to go through all the connection steps, and also need to find an inverter that's compliant with PNMs new requirement of IEEE 1547-2018.

Has anyone done something similar? or can point me towards any threads here that would contain details of this kind of set up, which inverters have dynamic bonding.
 

Attachments

  • Screenshot 2024-05-21 at 5.38.06 PM.png
    Screenshot 2024-05-21 at 5.38.06 PM.png
    246.4 KB · Views: 2
Last edited:
When researching while we were thinking of moving to Santa Fe one thing listed is a design and drawings stamped by a licensed electrical engineer.

Plans posted at entrance to the property, RSD for any panels on the roof, grid disconnect clearly marked and either at property line or at first point of entrance.

Maybe 8 rules to follow and each had many sub rules. But none of them much different than you would expect. All designed around poco personel or fireman safety.
 
Thanks, this is what we got from the County,
I've found out about the setback (which isn't mentioned in this doc) it needs to be 3ft on no less than 2 sides, I'm still calling around trying to get specifics the Manufactured Specifications (signed & sealed by Professional Engineer) part, the County engineers pointed me to the construction industry divisions department, I'm going to call them too see if I can get any details.

Do you think the grid disconnect part will still be needed if it's not capable of solar ever reaching the grid?
afaik the grid disconnect is a requirement from PNM, if this approach will work then in theory I have no need to interconnect with them or deal with their requirements, or at least that's how I'm understanding it at the moment (hopefully that's correct)
 

Attachments

  • PV Solar (dragged).pdf
    402.4 KB · Views: 2
  • Screenshot 2024-05-21 at 7.40.39 PM.png
    Screenshot 2024-05-21 at 7.40.39 PM.png
    193.9 KB · Views: 1
Do you think the grid disconnect part will still be needed if it's not capable of solar ever reaching the grid?
afaik the grid disconnect is a requirement from PNM, if this approach will work then in theory I have no need to interconnect with them or deal with their requirements, or at least that's how I'm understanding it at the moment (hopefully that's correct)
how would you connect the disconnect switch if you have no grid connection? An air gap of 200+ft is a pretty good "disconnect".

If you want a connection, but never export, then put a disconnect switch to keep them happy, and in case you ever do want to export.
 
cheers, it seems there'd be no requirements at all from PNM as we wouldn't be interconnecting, I like the idea of adding a disconnect switch into the design just incase we do ever need to go through the connection process.

The main thing I'm trying to learn at the moment is what type of inverters, and additional parts would be required to do the dynamic bonding set up shown in the video
 
It's very unlikely that any hybrid system would not be considered technically interconnected. In any case, dynamic bonding should not be necessary.

I run a double conversion system, with no AC connection to my battery and inverter, just a charger, and it all uses the existing main panel NG bond.

Still if I were to try to get it permitted, which is legally required, it would probably be considered interconnected.
 
I'm curious if anyone has looked at the EcoFlow Delta Pro Ultras with Smart Panel 2 set up to address this. The smart panel they provide is essentially a subpanel that can receive electricity from the grid or the Delta Pro ultra inverter. That inverter can bring electricity in from solar panels and has batteries connected to it. The smart panel can mix and match the source of electricity from the grid, the solar panels, or the batteries. This is what is known as grid assisted as you can receive power to the Smart Panel from the grid but your solar panels are not tied to the grid. The solar panels only provide electricity to the inverter and that electricity can be sent into the Smart Panel or the batteries. If the grid goes down, you still have power to your home in combination from the panels and the batteries. This is not what you would call an interconnection as you are not tying your solar panels to the grid itself. So I think this might be a way around all the pnm issues. I live in El Dorado at Santa Fe in the southern half of the division that is now yellow zoned by the power company and I'm looking at this as an alternative to trying to grid tie. Thoughts?
 
HI!

I haven't checked out the Delta Pro, the reason I'm looking at the 6000xp is because they are not designed to back feed the grid, so there should be no need for any interactions with PNM at all. I think all that will be needed is working through the requirements for the County, which looks like it may have changed? I just found this one
I'd been going by this one, which has additional requirements for an engineer stamp

Not sure which one is most recent or accurate!?


And the Eldorado HOA I think is mainly concerned with the visual appearance to other neighbors

The 6000xp seems like a great option as you can add additional units if you require more input/output capacity.

The part I'm trying to figure out at the moment is how to keep 2-3 heavy circuits connected to the grid and everything else on solar, without having to ask PNM to disconnect power whilst a new panel is put in.
I'm also monitoring our energy usage to see if we could maybe get away with running all circuits through 2 x 6000xp in parallel, I think that could handle 50 amps per 120v phase.

And sorry that about the PNM announcement, context for everyone else, PNM have just said they're almost at capacity in certain zones in Eldorado, so if you want an interconnection you have to pay $2500 up front just to be assessed for approval, I think that's it, please correct me @ecosee if that's wrong.
 
Can the 6000xp pull from the grid when solar is inadequate? What happens to those circuits when you didn't get enough sun?

The Delta Pro ULTRA has a smart panel that can accommodate 12 circuits. The grid becomes a backup power source when there isn't enough sun for those circuits. It prioritizes the solar panels first, the battery second and the grid is there as a fall back.

The DP-Ultra also does not back feed into the grid. It's "grid assisted" not "grid tied".

BTW - we're currently installing a full off grid eg4 system where I work. No grid available. It's 48v with 38 kW of their batteries and 7.2 kW panels. Can add photos in a couple of weeks
 
Last edited:
The DPU cannot export to the grid, but it can receive from the grid. It is not "interconnected". So you essentially have grid backup power when the sun isn't shining. I'm very curious about this system...
 

diy solar

diy solar
Back
Top