I have these panels:
My two EG4 6500ex inverters will take 4 strings of panels in series and has a max PV input of 4000 watts per string. Max VOC is 500 volts per string.
I'm wanting to connect 8 panels on a single string. Those calculations are:
460 watts per panel * 8 panels = 3680 watts
50.8 VOC * 8 Panels = 406.4 VOC
By those numbers I should be good. My question is on the bifacial gain (they will be on a pergola on a deck), which can spike up to 575 watts.
575 * 8 = 4600 watts.
At that point I am over the max wattage. Is this a safe amount of over-paneling, or should I limit the string to 6 panels?
Preorder - BlueSun 460W Half-Cell Bifacial Solar Panel (Silver) | Up to 575W with Bifacial Gain
Signature Solar provides solar panels, off-grid solar systems, grid-tie, and hybrid systems. Quality solar inverters, bifacial solar panels, complete solar kits, solar batteries. Featuring brands such as EG4 Electronics with their solar battery, LifePower4 and EG4 LLifePower4 and EG4 LL
signaturesolar.com
My two EG4 6500ex inverters will take 4 strings of panels in series and has a max PV input of 4000 watts per string. Max VOC is 500 volts per string.
I'm wanting to connect 8 panels on a single string. Those calculations are:
460 watts per panel * 8 panels = 3680 watts
50.8 VOC * 8 Panels = 406.4 VOC
By those numbers I should be good. My question is on the bifacial gain (they will be on a pergola on a deck), which can spike up to 575 watts.
575 * 8 = 4600 watts.
At that point I am over the max wattage. Is this a safe amount of over-paneling, or should I limit the string to 6 panels?