I was coming to the same conclusion.The 3rd string not showing any voltage is complete different issue, you probably have had only 2/3 of the PV power for a while.
I was coming to the same conclusion.The 3rd string not showing any voltage is complete different issue, you probably have had only 2/3 of the PV power for a while.
how much current is running through the 2 wires that do show voltage with the disconnect open, after you close the disconnect (switch it to on).
The 3rd string not showing any voltage is complete different issue, you probably have had only 2/3 of the PV power for a while.
Currently I would be mainly interested to see why the inverter complaints about low input.
I just checked all the white wires with red tape and they are at .02 Amps with the disconnect switched on All of the fuses were installed as well and inverter was powered offhow much current is running through the 2 wires that do show voltage with the disconnect open, after you close the disconnect (switch it to on).
The 3rd string not showing any voltage is complete different issue, you probably have had only 2/3 of the PV power for a while.
Currently I would be mainly interested to see why the inverter complaints about low input.
To make a better assessment:I just checked all the white wires with red tape and they are at .02 Amps with the disconnect switched on All of the fuses were installed as well and inverter was powered off
OK thanks, I'll check them tomorrow or Wednesday and report backTo make a better assessment:
1) there must be light shining on the PV panels, preferable a lot , let's say around noon.
2) inverter in the off position.
3) you must be seeing the 350 volt between the common and both the 2 strings with the disconnect switch open (off position)
View attachment 180005
Disclaimer: no graphical artist genes in my family, sorry for the bad altered version.
4) then you close the switch, verify the voltage now dropped down to 11 volt. (this is not normal in a working condition, but since you measured it before, i would like you to verify this)
Measure between P & N (Positive) and Negative aka the input to the inverter.
Extra information that might be interesting: when you switch it off again, open 1 fuse holder and switch it on again and see what voltage you are now reading between the common and the joined parts (P & N)
switch off again, close the open fuse holder, open the other fuse holder, switch on again and measure the voltage one more time.
switch off disconnect & close the second fuse holder
5) Switch on disconnect & measure the current flowing through the 2 white wires with red tape.
You haven't mentioned what panels you have so we have to make guess, but normally in a working condition, you should see multiple amps flowing through the wires. let's say in the 2-10+ amp range.
Scenario 1:
If the inverter has a defect and basically is a short circuit on the input side, you would see 11 volt and multiple amps flowing.
Scenario 2:
Inverter sees the voltage and wants to startup but for some reason there is a high resistance in the PV string, that would drop the voltage at the input to 11 volt but the current would be in the range you measured before : way below 1 amp: 1/10 or 1/100 of an amp.
That info is essential to draw a conclusion imo.
okay. without additional info, no idea yet.regarding the extra info, opening and testing one by one each fuse. I did this today and every time was the same. 11 volts but I'll do it again tomorrow.
I have those panels as well and I love them. Still going strong.Panels are sunpower SPR-220 Specs here: http://www.solardesigntool.com/comp...7/SPR-220-WHT-U/specification-data-sheet.html
Normally an inverter is powered from the DC (PV) side , not from the grid.Scenario 2: when you say the inverter wants to start up. I have the AC breaker off to it so it is assuming the grid is down and is completely off. Should I perform the tests with the AC breaker on? or it doesn't make a difference?
Measurements done,To make a better assessment:
1) there must be light shining on the PV panels, preferable a lot , let's say around noon.
2) inverter in the off position.
3) you must be seeing the 350 volt between the common and both the 2 strings with the disconnect switch open (off position)
View attachment 180005
Disclaimer: no graphical artist genes in my family, sorry for the bad altered version.
4) then you close the switch, verify the voltage now dropped down to 11 volt. (this is not normal in a working condition, but since you measured it before, i would like you to verify this)
Measure between P & N (Positive) and Negative aka the input to the inverter.
Extra information that might be interesting: when you switch it off again, open 1 fuse holder and switch it on again and see what voltage you are now reading between the common and the joined parts (P & N)
switch off again, close the open fuse holder, open the other fuse holder, switch on again and measure the voltage one more time.
switch off disconnect & close the second fuse holder
5) Switch on disconnect & measure the current flowing through the 2 white wires with red tape.
You haven't mentioned what panels you have so we have to make guess, but normally in a working condition, you should see multiple amps flowing through the wires. let's say in the 2-10+ amp range.
Scenario 1:
If the inverter has a defect and basically is a short circuit on the input side, you would see 11 volt and multiple amps flowing.
Scenario 2:
Inverter sees the voltage and wants to startup but for some reason there is a high resistance in the PV string, that would drop the voltage at the input to 11 volt but the current would be in the range you measured before : way below 1 amp: 1/10 or 1/100 of an amp.
That info is essential to draw a conclusion imo.
the way I understand it is there is a safety switch built in to the inverters. When the grid goes down the inverter shuts off to prevent backfeed to the grid.Normally an inverter is powered from the DC (PV) side , not from the grid.
But your inverter might be different.
Sunnyboy/Fronius I have are "dead" when dark and at the creek of dawn they wake up again.
I don't know enough about your inverter if that is also the case.
My diagnosis from this :Measurements done,
350V on lines 1 and 2
With the disconnect turned on voltage dropped to 15v
There are 4 white wires
wire 1 (connected to P) drawing 4 Amps
wire 2 (connected to P) drawing 4 amps
wire 3 (connected to P) drawing 0 amps
wire 4 (connected to N left of P) drawing 8 amps
I powered on the inverter with the AC breaker and see the same numbers
That is the case with all grid tied inverters: part of UL1741the way I understand it is there is a safety switch built in to the inverters. When the grid goes down the inverter shuts off to prevent backfeed to the grid.
My Fronius/SMA are completely dead, nothing on the LCD display when there is no light shining on the PV panels.we also have a fronius in front and it does the same thing. If I flip the ac breaker off the inverter shuts down. At night the inverters are in a standby mode until DC is detected
It sure looks that way.@FilterGuy do you agree with this ?
Thanks guys, Is it common to see this type of short on an inverter?It sure looks that way.
Try disconnecting the inverter from the junction box and see if the voltage goes back up on the junction box output.
As an aside: Someone might ask why the fuses aren't blowing if there is a short on the output. The answer is they are not designed to blow in this situation. The fuses are intended to blow if there is a short on the string and the other strings pump too much current into the short.
By selecting a wire that is sized to handle 1.55x the Array Isc, there can be a dead short on the combiner output and nothing will burn. The reason it is done this way is that the Isc and Imp are so close to the same that it is almost impossible to select a fuse size that would 1) do any good and 2) not blow during normal operations.
I don't know how common it is but I have heard of it before.Thanks guys, Is it common to see this type of short on an inverter?
I'll disconnect the inputs from the inverter and cap them off and test again.