Sorry can't send a screen cap from my mobile but here they are:
Battery Cap 560Ah
Charged voltage 52.8
This should be 0.2V below absorption voltage for solar OR 0.2V below float voltage for AC charging. If you have both, set for solar.
Discharge floor 0%
This is a "time to go" number. When the shunt reports the time to go, it's based on this setting. I prefer to set it to something like 10-20% since one can't always count on their battery delivering true rated capacity.
Tail 4%
At lower charge voltages, this need to be lower than the 4% default. I'd try 2%.
Charged detection time 3m
Peukert exponent 1.03
Charge efficiency factor 95%
99%
Current threshold 0.10A
Time to go averaging 3m
Battery SOC on reset Keep SOC
SOC 28.5%
My inverter is pushing it to 55.2 with this setting anyway.
so the shunt is reporting 55.2 even though you have the charger set to 55.0V? If so, that's fine.
A bit high.
Agreed. My reasoning though is our system goes for days and even weeks during the rainy season, for example, at the lowest SOC (unable to fully charge because we're using up all the PV power) and long term these batteries last longest if they are not sitting forever below around 20% SOC according to Luyuan, so I thought it's better to keep them at that level. No good?
That's a good reason.