Is it possible to run more than one gauge (where each requires a shunt)off a single shunt providing they each require the same size shunt?
Regards
Fred
Regards
Fred
Given the shunt is an extremely low impedance source you can put 100 gauges if you want. But you need each gauge to have its own wires if you want to keep the same accuracy
The gauge should be extremely high impedance, so there should be very little current through the wires coming off either side of the shunt, consequently, the voltage drop across those lines will be extremely low. You could *probably* get away with sharing those lines, but why take the chance. Do what @BiduleOhm suggest and run separate lines.
The Battery + connection to the shunt is just for routing B+ to the gauge through the common cable. The B+ is not used on the shunt.
Also, I need a slightly longer cable between the shunt and the gauge. I will be using shielded 2 twisted pair to make the longer cable.
Twisted pair 1: B+ and B- power wires.
Twisted pair 2: B- and P- Sense wires.
It will also be a heavier gauge wire than the original cable. (The original is 26awg)
Something I just realized, When I hook this up I need to put a small fuse where the B+ hooks to the battery. A short anywhere along those small wires will quickly turn them into smoke....and maybe fire.