Finished the electrical work to connect the generator to the inverters.
Won't qualify the AC2.
Firmware is 1.11.01bn49
Anyone else have AC2 qualify OK on this version of FW?
What did you do to make it work?
The countdown timer expires, AC2 LED on the inverter control panel is flashing,
just never goes to solid green.
After 10 minutes, I shut down the generator.
Inverters report AC2 numbers that should be good. WTH
Also:
- AC settings - I left AC1 as priority, can't see how this would effect qualifying AC2.
- "generator support - enabled
- "generator support plus" disabled - I can't find any documentation on "plus".
(I suspect "plus" is like "double secret probation", and no one @ Schneider tech support will know about it)
Won't qualify the AC2.
Firmware is 1.11.01bn49
Anyone else have AC2 qualify OK on this version of FW?
What did you do to make it work?
The countdown timer expires, AC2 LED on the inverter control panel is flashing,
just never goes to solid green.
After 10 minutes, I shut down the generator.
Inverters report AC2 numbers that should be good. WTH
Also:
- AC settings - I left AC1 as priority, can't see how this would effect qualifying AC2.
- "generator support - enabled
- "generator support plus" disabled - I can't find any documentation on "plus".
(I suspect "plus" is like "double secret probation", and no one @ Schneider tech support will know about it)