Last night/this morning was the first true test of my Senville 24k heating our cabin (monitoring remotely). It's installed on our main level which also has a loft, total main/loft level size is 1050sqft. I had the 6 electric baseboards set to 50F (backup) and the mini-split set to 67F. Got down to 18F outside by 7am ET. At that time the Senville was able to keep up but seemed like it was in a defrost cycle (peaks up to 3300 watt) which allowed the inside temp to dip down a few degrees. Outside of the peaks AFTER the 6am timeframe, average usage was around 1200 watts.
Other interesting results for 10/31maintaining 67F main level/loft (mini split only) and lower (electric baseboard only) from 12am-11:59pm:
Other interesting results for 10/31maintaining 67F main level/loft (mini split only) and lower (electric baseboard only) from 12am-11:59pm:
- Main Level (with loft) w/Mini Split (1050sqft): 17.6kWh
- Lower Level w/Electric Baseboard (825sqft): 54kWh