Started on my solar journey about a year ago and naturally looked at installing a small mini split to reduce the load on my main HVAC. I have run into a number of issues and a couple of solutions that you may find helpful.
Installed the Leto model of Senville's 12,000 btu unit with 110v. Went with 110 to make running power a little easier but beginning to regret that decision. I chose the LETO as its cheaper than the more expensive Auro version by about $600. Aura also requires 220V.
Then the fun began. Install was easy enough. I flared my own lines for a cleaner install and bought my own vacuum pump for about $100. Only installation issue is that I did not wear gloves when vacuuming the lines and the hose adapter was sticky. Almost froze my fingers off trying to get it off and lost some 410a in the process. Was able to correct this though.
It was the beginning of spring and the unit was cooling well but when the outside temperature spiked the indoor unit would freeze over and start spitting ice. As summer started this became a common occurence. Senville sent me a new control panel but it didnt help. Turned out that the fan on "Auto" would not run fast enough for proper air flow. When I set fan speed on "high" it worked great with no more freezing. However that defeats the purpose of an auto fan and I found myself manually resettig fan speed every day.
Winter has just set in and the Leto is supposed to provide heat down to 5F according to their Amazon information. It does not! Stops heating at 32F. This is very disappointing as its not going to supplement my heating as much as I hoped. I live in Upstate South Carolina and pretty common to get into the 20s and 30s at night.
Apparently the Aura version will heat down to -22F. I also have found that the Pioneer Diamante 230V also have an auxilary heater strip that will work down to -13.
Its not worth the time and effort to replace the unit but knowing what I do now I would opt for the Aura and run a 220V line.
Installed the Leto model of Senville's 12,000 btu unit with 110v. Went with 110 to make running power a little easier but beginning to regret that decision. I chose the LETO as its cheaper than the more expensive Auro version by about $600. Aura also requires 220V.
Then the fun began. Install was easy enough. I flared my own lines for a cleaner install and bought my own vacuum pump for about $100. Only installation issue is that I did not wear gloves when vacuuming the lines and the hose adapter was sticky. Almost froze my fingers off trying to get it off and lost some 410a in the process. Was able to correct this though.
It was the beginning of spring and the unit was cooling well but when the outside temperature spiked the indoor unit would freeze over and start spitting ice. As summer started this became a common occurence. Senville sent me a new control panel but it didnt help. Turned out that the fan on "Auto" would not run fast enough for proper air flow. When I set fan speed on "high" it worked great with no more freezing. However that defeats the purpose of an auto fan and I found myself manually resettig fan speed every day.
Winter has just set in and the Leto is supposed to provide heat down to 5F according to their Amazon information. It does not! Stops heating at 32F. This is very disappointing as its not going to supplement my heating as much as I hoped. I live in Upstate South Carolina and pretty common to get into the 20s and 30s at night.
Apparently the Aura version will heat down to -22F. I also have found that the Pioneer Diamante 230V also have an auxilary heater strip that will work down to -13.
Its not worth the time and effort to replace the unit but knowing what I do now I would opt for the Aura and run a 220V line.