The capacity is 100% at the time that I disconnect the solar from the house each day. That is what the 10 120v circuits in the house use in that 8hr time period. when I know that it will be a strong sunny day, I turn it on early, maybe an hour or 2 before the sun is on the panels, knowing that it will catch up when the sun hits the panels. The panels produce about 60 amps in full sun. As you can see, I am only producing about 5amps right now, 2 of which is going to feed the hungry inverter. 60 amps is not the case this time of year.
If you have a "strong sunny day" where the PV supplies all the energy, then yes, the shunt will correctly read 100% until you draw from the battery.
So, do I hear you saying that the shunt voltage readings could be out of calibration?
I'm saying it needs to be verified.
The shunt does nothing but measure. But the settings for the shunt can determine the accuracy of the readings that are stored. It appears that the 100% SOC can be set. I have done that a few times when I FELT it was the right moment. But, what determines when I should push the 100% State of Charge Synchronize button?
Usually never. If you have the shunt programmed correctly, and it syncs/fully charges at least a couple times a month, it should be accurate enough.
The system is NEVER at a quiescent point with everything connect to where I can definitively say, the battery voltage is 100% and the current is 0, meaning the charge controllers are now still charging.
On 3/22, this was certainly fully charged:
Zero Current Calibration, in my estimate, can only be done by disconnecting any possible load from it before pressing the Calibrate button.
Correct. You could disconnect everything from the system side of the shunt. You can also verify the current measurement with a clamp DC ammeter if you have one.
The question that still haunts me is this. When the SOC says 95%, how can the batteries be depleted? If I have a 400Ah bank that I can use to 50%, then I should have 200Ah usable power. RIght? Is part of the victron system that is doing the math going by the number of Ah used until it gets to an assumed 50% or is it making its calculations on battery voltage at any given time? Obviously, since a shunt is a current measuring device, and the shunt is connected to the "Voltage Level" of the bank, it stores voltage and current readings at the sample rate and the app or the VRM does the math on the the data.
I have some quality multimeters and will take some readings and write them down. I have no history log book of readings. Pretty much all in my head.
A shunt can only accurately reflect a battery that complies with it's programming. You are ASSUMING that your system is properly connected, configured and meets specification. There is STRONG evidence that your assumption is not correct.
As seen in this screen shot, the voltage displayed could be determined as a rising voltage within the BULK charge mode. It is also within the range of the FLOAT voltage range. Bulk is pushing regulated current toward the Absorb voltage level. But, since the Consumed Ah is not zero, I have to assume that the system is in Bulk. There just isn't enough current to push the voltage up to the 28.2 to 29.4 volts that victron specifies on its site to push the charging into Absorb.
It doesn't matter much. Your battery is poked full at 8-16A and the absorption voltage. Being near the absorption voltage and only pushing 2.5A means you're very nearly fully charged if not fully charged.
If you have been watching the charging of the battery bank today you have noticed that the Consumed Ah has only gone from -16.90 to -8.50 today. Not much charging going on. No sun, not even once for a little while.
Yep.
I am sure there is some device that Victron has that can be connected to the output of the CC to measure current produced. The shunt only measures net current. Current made minus current used..
Yes. It's another smartshunt configured as an energy meter mounted between the MPPT and battery. Doubt you want to do that.
The Cerbo GX allows me to monitor the system without sitting on a stool in front of the electronics cabinet in the front yard (watching electrons go by.... or do you count the holes going the opposite direction.) I guess it depends on which way an engineer measures current flow.
I get confused by this as well.
Looking at the remote console on the phone app, there is space for other sensors such at AC inputs, AC loads, and of course, it says my system is OFF. Maybe that is my whole problem!
How do I turn it on?
No. It says the inverter is off. You don't have a Victron VE.Bus inverter connected, so the GX assigns it the "OFF" state.
You will also never see a number in AC in or AC out as those are based on what's connected to the VE.Bus inverter... that you don't have.
I supposed another shunt could be connected in line with the CCs and connected to the Cerbo GX, but I don't know if the Cerbo can facilitate 2.
Yep. Per the above. It can accommodate up to 15 VE.Direct devices with the 4th-15th connected via a VE.Direct to USB adapter and a USB hub plugged into the Cerbo.
Installing a smartshunt as an energy monitor is a very common practice. You can even name it "MPPT".
In closing:
- There is strong evidence that there is a problem with your system as listed in my prior post.
- How did you test the batteries as you indicated? What were the results?
- You bought a new tester. Link?