Please read the controller manual closely so you know what the Amp rating actually is.
The following describes the Victron Line of SCCs. Other brands may be different.
The Victron MPPT solar controllers are listed with a voltage and current: Example
Smart Solar 100 | 50.
- The 100 is the absolute max voltage that can be applied to the PV input connections (100V in the example).
- The 50 is the maximum current the SCC will generate on the battery output connections (50A for the example.
So, for your 2x305=610 watts, we need to know the system voltage so we can calculate the current at the output.
- 12V system
610W/12V=50.83A
- 24V system
610W/24V = 25.41A
- 48V system won't work. (The PV voltage is too low).