Small Home ongrid, get AC offgrid
trad
TX
I use about 1000kwh per month, but the bulk of that is AC here in S Texas. The goal is to put the 3T 240v AC on solar while the sun is shining. When the sun goes down, the AC can switch to the grid.
I will make this investment looking for a quick payback, so large battery banks are out. I have room for 100 solar panels if necessary but I need to choose an All in One inverter, solar charge controller. What is the best 240v AIO that can use as little battery as necessary and seamlessly switch over to grid power when there isn't enough sun?
(the EG4 6500ex is awesome, but wouldn't that be overkill for this small load?)
(would this be a good use case for the much maligned Growatt 5000 ES ?)
So you think I should upsize the inverter and go for more loads in the house. The 120v fridge would be next for priority to move offgrid. Then some computer and internet loads are also 24x7 and would be next.
Things like the microwave, toaster, kettle etc are all high power draw, but not used frequently. I don't mind paying for electricity for these type of loads.
Better invest in some soft starters for the AC too or the system will have to be way oversized.
This was what I was hoping.
But Sig Solar says this for SPF5000 ES "Please note: We recommend using this inverter with batteries."
No batteries required for a single unit, in SUB mode.
Which would do what you described that you want.
With no batteries, how do you deal with, say a cloud rolling by and dropping the solar output for some time period? Do you just overload on panels and not turn the AC on until there is plenty of power available? There must be a tradeoff calculation between the cost of extra panels and adding some battery.
So the only issue might be start up load to spin up the AC compressor. Thankfully the AC has an LG compressor installed last year. Maybe it will have lower inrush startup loads.
Either it will, or it won't
What would you recommend ? Small battery with large amp BMS to allow for this?
The grid handles anything that the solar doesn't.
The grid handles startup surge.
I just looked at your signature, and see that you have heaps of 5000ES experience. I'm guessing you are using them with auto converters for split phase loads as well in spite of what Will recommends.
How well does the 5000 ES scale when daisy chained. Is this difficult to do?
For a split-phase output.
an Autotransformer is fine, for no grid connection.
If also connected to grid, an isolation transformer is the best option.
You can stack up to six. It's very simple.
I would install an EG4 18kPV or Solar-Ark 15k. Have it wired to the whole house. 1000 kWh/mo is about 33 kWh per day, which is typical for a mid-sized house. You can add solar as needed. Set for zero grid export, or export excess if net metering. Add batteries if you ever want it.
If you don't have net metering, some batteries can be beneficial to provide power into the evening (time shifting energy production).
or a separate 120v solar AIO for the 120v loads?
Probably depends how much wattage you have in terms of 120v loads. 120v loads over 3kw generally require multiple inverters in parallel, at least if you're talking all-in-ones. There are some outliers but if you are trying to get going for the cheapest price then two separate AIO's for 2 separate voltages is probably not it.
The refrigerator would be the obvious steady state load. The kitchen counter loads are bursty, and the grid is well suited for bursty loads.
The one Sig Solar lists alongside the 5000ES is the
ATS 5000T-ES​
They don't specify, but the forum is calling it an auto transformer. I don't see any isolation transformer on their site. What would I be looking for?
ATS 5000T-ES​
They don't offer an isolation transformer.
Used from places like Ebay is the cheapest option.
You're looking for a 240v input (most commonly 480v/240v) and a 240v/ 120v output single phase transformer.
Size should be 5kva per Growatt SPF-5000-ES.
So, 10kva for 2 stacked Growatt's.
Like this?
5kva transformer
This looks perfect, but sadly the forklift doesn't come with it.
Is this typical size and weight for a 5kva?
Like this?
5kva transformer
You don't need hospital grade. (Extra large and heavy) And that one doesn't have an enclosure. (You need it enclosed)
But, it is a hell of a good price.
Also, unless you have 208V and want 120V, don't know what good that transformer would do you.
What are you trying to accomplish? Start with single-phase 240V from an inverter which sometimes has grid L1/L2 passing through, and create isolated 120/240V?
Standard power transformers don't play nice with inverters. They have no-load current about 10x what is desirable, because they are sized allowing core to go part way into saturation every cycle (saves money and weight).
They are much better behaved at 1/2 of rated voltage. Easy to use 240/480 primary as 120/240V autotransformer. But to make an isolation transformer I would need two. 240/480 primary in series gets 240V from inverter. 120/240V secondary makes 120V L1 for load. A second transformer wired similarly makes the other 120V L2 for load.
Why not have batteries?