Hello, did you resolve your issue? I have the same question, where does the grid sell come from? When doing grid-tied it comes straight from solar panels right, but for this setup you now have a battery installed, so hybrid setup now....
The question is that how did Sol-Ark explain the setting for the grid sell to come from solar panels ONLY, and not from the battery cause the point of the batteries are for backup, it shouldn't be used to sell back to grid too.
This is the method to use if you only want extra PV power to be sold to the Grid and Not Sell Any Battery Power.
If your doing it on the web interface then you would go into (
Equipment-Inverter-Parameter) settings and then go into Work Mode.
Once in work mode turn on the "
Solar Sell" Option. Next set the "
Maximum Power Sell" which is the Max amount of surplus power that you want it to send from the PV to the Grid. If your doing this from the LCD screen then you would turn on the "Limited Power To Home" Mode and the "Grid Selling" option and then set the Max Power. Both methods achieve the same thing.
Once this is done it will now sell power to the grid whenever excess PV is available.
This is the method to use if you Want Battery Power Sold to the Grid.
If you want to sell power during the Night to say do peak shaving then you have to do all the same things as above but now you have to click the needed "
Sell boxes" for the TOU. So lets say your TOU slot
#6 runs from 8pm to 3am and you have it set to use the battery SOC down to 50% and the usage is set to 2000 Watts Max. If you Click the "
#6 Sell Box" and turn it on, now your TOU #6 setting at 8pm will start selling power to the grid until 3am.
If you leave the 50% setting and the 2000W setting then what will happen is that if your house is using 1200W at 8:15pm it will Send the extra 800W to the Grid as Sell back power, so only excess battery power is sent to the Grid. If you want it to sell a constant 3000+ Watts to the Grid then up your "Power" box from 2kw to 5kw and now you will have roughly 3kw being pushed to the Grid until the battery reaches 50% SOC and it will then cutoff battery power and you will be drawing all your power from the Grid or PV if it is available.
Keep in mind a power outage overrides all these settings and the Sol-Ark will of course stop Grid selling and pull as much power from the battery as needed (up to the Max Battery limit you set) to power the Critical Loads Panel