Finally installed the 100 amp main breaker in the CLP once I got a time slot from my wife where I could shutdown power, took half an hour
and began filling in wires into the generator 6 space service panel. Placed it on top of the raceway, in the center. When 2nd XW Pro is installed the panel will be under the XW Pro. Incoming vents on the XW Pro are on the front bottom panel of the XW, so air flow should be fine
Ran #4 wires from that panel to the 2 60 amp generator breakers inside the PDP. Each of those 60 amp breakers will feed 1 XW Pro
Used a spare 80 amp QO breaker on the #4 wires. Will use #4 all the way out to the generator - who knows, I might get a 15kw generator someday. and it is 50 ft to the generator spot.
Added a 30 amp 240 v receptacle on that generator panel as well. So I can use grid or generator to run a 30 amp generator circuit to feed a future EG4 Chargeverter.
That leaves 2 more slots in the panel, which I just filled with a 60 amp QO breaker I had.
Might install a 50 amp receptacle and a 50 amp breaker from the generator, for the fun of it.
l will work my way upstream to the generator from the panel, by adding conduit and wire over time until I finally get to the generator location out side
Next NEW wire will be the #2 from the Grid service panel upstairs down to the grid 6 space on the upper left.
28 feet of distance, with 3 wires cost is some $220. That is from
Enter the desired footage below:
www.wireandcableyourway.com
This is the cheapest I have found, though shipping starts at $22. Copper price is getting bad. Already got the ground wire.
Current picture of the AC side and inverter with new generator panel.